Discuss Immersion on ring main. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Hi I'd appreciate some help with a Pir that I've been asked to do on 6 flats converted in September 2008. I have been in one to sort out a tripping problem on the ring main.After much frustration it turned out to be the immersion heater that was faulty and was tripping its rcd.Here lies my problem. The immersion is the only source of hot water heating, it has been put on the ring main and this contrary to both Building and Wiring Regs when it was converted.How it got through a visit from the LABC is another matter.They possibly passed it because the the central heating is on its own circuit (also electric) and they didnt look any further.Advice on what code to put it on would be appreciated can a 1 be justified or is a 2 better.Either way I think the owner is going to go ape with the electrician who installed them all.
 
Last edited:
Just a note. The immersion heater can be on the ring main, providing the vessel is less than 150 Litres.

Think you`ll find thats 15 litres. Anything more requires it`s own circuit.

As stated, Code 2 rather than 1.

Still warrants an unsatisfactory

and let the spark who did it take the heat (no pun intended) & not you
 
Last edited by a moderator:

Reply to Immersion on ring main. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
503
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock