Average lifespan of reputable inverter

  • 5-7 years.

    Votes: 3 12.5%
  • 8-10 years.

    Votes: 3 12.5%
  • 11-14 years.

    Votes: 10 41.7%
  • 15-20 years.

    Votes: 6 25.0%
  • Over 20 years.

    Votes: 2 8.3%
  • Don't know.

    Votes: 0 0.0%

  • Total voters
    24
  • Poll closed .
Interesting thread. Not all inverters have/need internal forced circulation of air to cool down internal components. Using high quality components and a design focused on efficient layout of internal power-flow and passive air flow etc can avoid unwanted hot-spots internally thereby prolonging the lifetime of the inverter overall. A good quality unit that is matched adequately to the system should be good for 15+ years quite easily. Most top of the line string inverters have 10yrs warranty by default, with options to increase to 20yrs if required.
 
There will be a lot of PV systems sat on roofs with failed inverters that customers just wont have the money to repair.

Yes, that's a concern and that's why, since I came onto this forum, I have advocated a "depreciation" allowance as a margin of safety, since the customer can't get the money back like in a bank account, and in order to continue earning FiT payments and enjoying bill savings when the system gets old, they may need to have built up a cash reserve to pay for repairs to keep the old girl running.
Solar PV owners should use about half of the FiT payments in the first five years to build up a repairs fund just in case they're one of the unlucky ones whose inverter fails in years 5-7. Such a "rainy day" fund is desirable anyway, since it might be the car which needs repairs, or the boiler - all of which can amount to hundreds of Pounds quite quickly.
 
I would expect string inverters to last around the 10 year mark, considering the positioning of most in lofts which are generally more dusty and very very warm! It also depends on the client, as the majority will have forgotten about the inverter after 5 years and probably would never even check on it. Though by the time they do fail, the cost of a new one would be considerably less than now, I would hope anyway! The cost-benefit of just changing it to purchasing warranty makes it a no-brainer in my opinion right now.
 
Not having any knowledge about typical location of inverters I was quite surprised to read above that they are frequently installed in lofts. Most lofts I've seen are a bit of state, so whether from dust, rodent, ambient temperature or fallen junk, it's a harsh environment for such an expensive piece of kit. FB - your idea is a good one.
 
The inhernet inverter weak spot IMHO is the quality and type of capacitors installed inside them, aside from the human factor and innapropriate system design /installation.
I expect to see 1 or 2 Inverter failures in the first 20 years of service.
 
I don't think inverters failing outside of their warranty will be a big issue - judging by pricing trends I would say that in 5-10 years they will cost significantly less than they do now, and probably be a little more efficient.
 
Interesting! where does it get its air from then? does it circulate the air within the inverter which would be pointless or does it draw it from outside the enclosure leaving you with a fan that will still "clog up and fail" but is not user servicable.
If the cooling fan is so critical why are inverters often installed in loft spaces where the ambient temperature can easily hit 50 degrees, just when the inverter is working hardest. That has got to be a recipe for a shortened lifespan.

I am on my second TV in 7 years and this one has had to be repaired due to an inherant capacitor problem.

There will be a lot of PV systems sat on roofs with failed inverters that customers just wont have the money to repair.

I think most customers could afford it, considering the initial outlays and returns they will be getting. Repairing one for £100-£150 is not going to break the bank.

Regards TV's, you've been unlucky. If I were you, i'd take out extended warranties.
 
Interesting! where does it get its air from then? does it circulate the air within the inverter which would be pointless or does it draw it from outside the enclosure leaving you with a fan that will still "clog up and fail" but is not user servicable.
it's designed to blow heat off the components and onto the reverse side of the heat sink on the front of the inverter, so doesn't draw air from anywhere it's just recirculating the internal air.


If the cooling fan is so critical why are inverters often installed in loft spaces where the ambient temperature can easily hit 50 degrees, just when the inverter is working hardest. That has got to be a recipe for a shortened lifespan.
yes, it will virtually always shorten the lifespan to some extent, but using inverters that are designed for higher temperature operation, fitted with higher quality capacitors, and either fitted with internal fans protected from dust, or easily replaceable fans, or even passive cooled reduces this impact, and I'm relatively confident should result in a 25-30 year optimal lifespan turning into a 15-20 year lifespan on average.

Depending on the airflow, temperature and dustyness of the loft of course, but the panels covering the south facing roof aspect does significantly reduce the peak temperatures, and we try to install an additional tile vent above the inverter if ventillation isn't too good, to reduce the worst of it.

I am on my second TV in 7 years and this one has had to be repaired due to an inherant capacitor problem.

There will be a lot of PV systems sat on roofs with failed inverters that customers just wont have the money to repair.
that's why cheap and nasty inverters with cheap capacitors are to be avoided like the plague, though it's not always obvious which makes this applies to.
 
A good indication of expected life is the price of extended warranties. Anyone who is good on the horses should be able to work out what the odds are of an inverter failing and needing to be replaced based on current cost. Just like bookies the warranty companies are in it to make a profit.
 
A good indication of expected life is the price of extended warranties. Anyone who is good on the horses should be able to work out what the odds are of an inverter failing and needing to be replaced based on current cost. Just like bookies the warranty companies are in it to make a profit.
to some extent, but as detailed above, the lifespan is dependent to a large extent on it's location and if it's ever dusted / fan replaced etc, so the inverter warranties will be based on pretty much worst case scenarios IMO.
 
This is almost like one of those answers on QI. Nobody knows. I always tell prospective customers that it is likely that the inverter will need to be replaced during the life of the system and build an appropriate cost plus inflation in to the PVSol economic model to cover.
 
From experience I would say that inverters with a transformer built pre 2008 can last well over 20 years - I'm talking about SMA SWR 750 - 2500 type inverters. Some that I installed 17 years ago are still working fine - quite a few fitted into lofts - and I've worked on a few that were installed before i joined the industry too.

The main reason is that these old style (G77 era) inverters used good solid components that were properly soldered.

Modern TL inverters are built down to a price with tiny, flow soldered components components, that are far more susceptible to heat and (more importantly) transient voltages. They are inherently less robust.

We used to tell our customers that a good inverter will last 12 - 14 years. Now we tell them 5 - 10 years.

You cannot choose according to brand name either. Fronius are crap. Every single one we fitted after 2010 has failed within 4 years. Mastervolts are almost as bad.

ABB / Aurora inverters had a bad batch from 2008-ish that all failed (E031 - due to soldered components failing in 'unpredicatble' UK temperature fluctuations...) after about 4 - 5 years. And it takes on average 4 - 8 weeks to get a replacement from Italy.

SMA's TL's now last on average 5 years and 6 months, but we had a period of one year where we stopped fitting the SB2500 because of a 99% failure rate. So even amongst one manufacturers range there can be problems. This issue was compounded by SMA denying any issues - even when presented with our installation / failure figures.

The Solarmax S range was bullet proof - the P range all failed within 4 years (probably why Sputnik went bust).

We've only had 2 failures out of all the Samils we've installed some of which are coming up to 10 years old now.

We recommend the fitment of SPD's for anyone with high average voltages (so next to railways, sub-stations - or anyone who lives in Cambridge where we regularly see 260 V mains) - certainly for micro inverters but increasingly for string inverters too. Not that every customer takes that recommendation.

Don't get me started about micro-inverter failures... !
 
Woken from hibernation by an email.......

It's now almost five years since my panels were installed.

Power One Aurora PVI-3600 (indoor version), in downstairs utility room.
8+7 (two strings) Kinve KV250-60M panels (3.75kWp) facing ESE at 40 degrees.

FiT payments so far totalling around £8k. Bill savings hard to quantify. Almost certainly reached 'payback' point with 20years of FiT licence remaining (subject to political interference).

Generation averaging about 3300kWh per year; worst year around 3100kWh, best year around 3500kWh.
Generation tends to be mean-reverting, so if we have an unusually dull spell (small FiT claim in one quarter) it's very often followed by an unusually bright spell (high FiT claim the next quarter).

No noticeable loss of generation as the system ages although variable weather patterns could mask a gradual decline for a few years.
Winter tends to see most days generation below average, with a few bright days pulling up the averages.
Summer tends to see most days above average, with a few very dull days dragging down the averages.
Spring and autumn tend to have a roughly equal mix of above-average and below-average generation.

The only 'problem' is that a couple of years ago the inverter lost its date and time settings, and I know someone else with an identical inverter of similar age that has the same issue.
I haven't investigated because everything is still working and I've been short on time, but I wonder if it might be as simple as a small button-battery needs replacing as is commonly found in electrical devices to retain date/time when they're switched off.

Cheers,
F
 
I've not pulled my Aurora apart but I'd got the distinct impression from the noise and the size of the air inlets on the indoor version, that the fan would be along the lines of a PC fan.

ABB / Power One UNO's and TRIO's - 3.0, 3.6, 10.0, 12.5, 20.0, 27.6 use passive cooling - therefore no fans. The IGBT s are strapped against the heat sink and use air convection for cooling. The newer TRIO's - 20.0 and 27.6 have a small fan inside to cool a capacitor set on the A/C filter boards, but that's it.

Fronius use active cooling method. So a smaller heatsink and therefore unit. But a fan helps the heatsink to convect heat.

I'd say an inverter should last around the 10-15 year mark.
 
ABB / Power One UNO's and TRIO's - 3.0, 3.6, 10.0, 12.5, 20.0, 27.6 use passive cooling - therefore no fans. The IGBT s are strapped against the heat sink and use air convection for cooling. The newer TRIO's - 20.0 and 27.6 have a small fan inside to cool a capacitor set on the A/C filter boards, but that's it.

Fronius use active cooling method. So a smaller heatsink and therefore unit. But a fan helps the heatsink to convect heat.

I'd say an inverter should last around the 10-15 year mark.

The 2011-model Power One Aurora PVI-3600 (indoor model) that I have definitely sucks in air (top left) and blows out air (middle right). The groan/whine of the fan starts when internal temperature rises to 50'C and stops when it drops to 40'C.
 
The 2011-model Power One Aurora PVI-3600 (indoor model) that I have definitely sucks in air (top left) and blows out air (middle right). The groan/whine of the fan starts when internal temperature rises to 50'C and stops when it drops to 40'C.

That is a PVI-2000 I believe? I was unaware they had a 3.6KW version?

But yes your right those units have active cooling and hence are a lot smaller.
 

Reply to Inverter Lifespan in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
978
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
496
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock