Discuss Led's in the UK Electrical Forum area at ElectriciansForums.net

N

nc12345

Hi guys

This main seem like a silly question but I'm not that up to date with all the led's etc
A client has asked for 3 led spike lights at the bottom of his garden.
Are there restrictions as to what length of cable you could run from a driver ?
For instance could a driver sufficiently supply three led's 25/30 metres away ?

Cheers guys , thanks to any replays in advance
 
With a low voltage the current is greater and this will mean more volt drop, so a long length of cable could well mean that the voltage is too low to operate the LEDs.
If possible try and keep the voltage at 230V as long as possible and fit the Tx as close as possible to the lights (or use really thick cable!).
 
Hi guys

This main seem like a silly question but I'm not that up to date with all the led's etc
A client has asked for 3 led spike lights at the bottom of his garden.
Are there restrictions as to what length of cable you could run from a driver ?
For instance could a driver sufficiently supply three led's 25/30 metres away ?

Cheers guys , thanks to any replays in advance

Put the driver in either an outdoor driver or put it in an ip rated adaptable box closer

Check the manufacturers instructions for max distance after driver
 
As a guide keep the 12v cable to around 6". Anything over 2ft will cause the voltage to drop low enough the LED won't work


i have a range of waterproof drivers available or put one in an adaptable box


Take not drivers require constant cooling! So a waterproof driver is always better
 
Cheers for the advice guys
I found a table on line which had cable sizes , lengths and wattages.
It states15w at the end of a run ,1.5mm will work up to 27m or 34m if dropped down to 12w
I was going to mount the driver in an IP box anyway to maximise the run
thanks again
 
As a guide keep the 12v cable to around 6". Anything over 2ft will cause the voltage to drop low enough the LED won't work


i have a range of waterproof drivers available or put one in an adaptable box



Take not drivers require constant cooling! So a waterproof driver is always better

6 inches max? You're joking right? Daz
 
12v halogens are more problematic but led wattage is so low you can get away with a lot further distances

I powered 14x 3w led at varying distances around a swimming pool to about 35m with 4mm SWA and was no problem at all
 
12v halogens are more problematic but led wattage is so low you can get away with a lot further distances

I powered 14x 3w led at varying distances around a swimming pool to about 35m with 4mm SWA and was no problem at all

35m isnt a very long distance to worry about volt drop.

For example in osg it recomends 50m for radial and 100m for ring
 
Yeah, but the whole thread has been about low voltage LEDs. Daz
 
I was just trying to make the point (with reference to your quote about ring main/radial lengths) that volt drop calcs will be a hell of a lot different at 230v to 12v.
 
If they're constant current drivers (and the LEDs are suitable), they'll compensate automatically for volt drop up to a point, dependent on the maximum output voltage of the driver.
 

Reply to Led's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’ve have some ten year old Collingwood SL020 RGB led garden spike lights which I’d like to keep using but wondering if I can use them with...
Replies
0
Views
643
Hello all. I want to fit LED strip lights to the ceiling with 45 degree channeling and diffuser around my son’s room. As there are so many...
Replies
3
Views
1K
Hi Guys n Gals, I'm a little stumped on a job and was wondering if anyone could advise? I've got 3 drivers going to 3 sections of garden lights...
Replies
21
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, This is my first time posting something on this forum. I'm busy putting together a design for some LED lights that are going to be...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock