I have an outbuilding a fair distance from the house. In this outbuilding I just want to have some lights, a small music radio/clock, and a receptacle for very occasional use of a power tool (such as a circular saw).

The distance to the sub panel would require about 400 feet of wire to connect the main panel to the sub panel.

Below is my thought process. Let me know your thoughts:

150-A Main Panel with a 50-A 2-Pole Circuit Breaker with a 4 AWG pigtail into a Polaris Insulated Tap Connector, connecting the 4 AWG pigtail to 1 AWG XHHW-2.

~400 foot run of 1 AWG XHHW-2 underground in PVC conduit to the sub panel. This 2 inch PVC conduit contains four 1 AWG wires (3 conductors and a ground)

Sub panel will have a 30-A main breaker, again with a pigtail connecting 4 AWG to 1 AWG via a Polaris connector.

The subpanel then contains a 15-A breaker for some LED lights, and a 20-A breaker for a receptacle.

Thanks
 

Reply to Long Distance to Subpanel in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, I have a Leviton 51120-1 SPD connected to a residential (120/240V) 200A breaker/service main panel – The 51120 is fed from (2qty) – 20A...
Replies
3
Views
775
I would like my plan checked by a professional. This project is a semi-open pavilion with a load center approximately 100 feet away. I am rating...
Replies
0
Views
699
I have an old 1959 house that appears to have outside service panel feeding 2 subpanels in the house each with only 3 wire feed. One subpanel(A)...
Replies
3
Views
843
  • Locked
Here is my set up. I have 100 amp service coming into my house into the panel box. I have a 50 amp subpanel in my garage fed from the main...
Replies
4
Views
991
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock