Reaction score
2
Ive just moved into a small house with a small out building without power. In the crawl space there was 8/3 12 meters and 20 meters 10/3 outbuilding is 26m. I purchased PVC 1” conduit and ran it to a sub pnl put a 2 pole 20a breaker in main pnl and 15a in sub with plug nippled to pnl. Here’s the question i ran a grinder the other day why does the breaker in the main pnl trip not the sub
 
Ive just moved into a small house with a small out building without power. In the crawl space there was 8/3 12 meters and 20 meters 10/3 outbuilding is 26m. I purchased PVC 1” conduit and ran it to a sub pnl put a 2 pole 20a breaker in main pnl and 15a in sub with plug nippled to pnl. Here’s the question i ran a grinder the other day why does the breaker in the main pnl trip not the sub
What size breakers are you using in main and sub panels?
 
Seems you are in Canada so maybe some more local folks will know, but here in the UK/EU breakers have two ratings:
  • Main current limit (e.g. normal current 'In' = 20A) which is slow & thermal in operation, typically starting at around 135% of In and getting faster with rising overload
  • The "instant" magnetic trip which comes in at different ratios depending on the "curve" selected, so B-curve =3-5*In, C-curve = 5-10*In and D-curve = 10-20*In
So for stuff with a high start surge you would go for C or maybe D curve MCBs, but base the 'In' thermal rating on the current-carrying capacity of the cables, sockets, etc.

Do not change the main breaker termal limit until you have established a replacement still provides adequate protection from faults and overload for the circuit(s) it feeds!

Again, I don't know the Canadian regs, but here you would need to determine that the current rating provides protection against overload (for socket outlets) and the MCB trip curve to protect against faults (e.g. short to earth/ground) by disconnecting in under 0.4s (typically it means the instant trip has to be less than the prospective fault current at the end of the wire, from the supply volts and earth loop impedance)
 
Also forgot to ask if the main panel breaker is a GFCI type? That might be a very different reason for it tripping.

Generally if you have two breakers in series you won't get very good selectivity (the ability of the down-stream one to isolate the fault without the up-stream one noticing). Manufacturers often publish selectivity tables showing combinations of their own breakers and what sort of fault level gives to the wanted outcome of only the final one tripping, but if it is a mix between two makes or very different families there is usually no accurate information about what sort of outcome can be expected.

Do you have the details of the two breakers (make & model)?
 

Reply to Main trips in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have an outbuilding a fair distance from the house. In this outbuilding I just want to have some lights, a small music radio/clock, and a...
Replies
0
Views
556
After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
677
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
600
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock