Discuss Minor works certified with no RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Isn't changing an RCD or fitting a new protective device considered an alternation and therefore not minor works? It requires an Electrical Installation Certificate.

Also the old BS 4293 ae no longer compliant with BS 7671 and should be replaced if major alterations are taking place.
I don't think there is one part of this post which is correct or valid. I hope your are not giving this advise or completing EICRs with such comments.
 
I did say it was only to be changed if major works were undertaken. For minor works I agree it would not be required.

And it would have been clearer if I'd said the BS4293 had been superceded rather than non compliant.

But I'm sure changing a protective device or adding one isn't covered under minor works. Page 418 of the regs.
 
Last edited:
I did say it was only to be changed if major works were undertaken. For minor works I agree it would not be required.
I have done works which you could consider more than minor and left BS3871, BS4293 etc.. in situ.
 
Interesting to google the question is adding an RCD minor works. Lots of differing views.
My view is it falls outside minor as a change to the fixed wiring and normally related to the distribution board.
But interested to hear views both ways.
 
Interesting to google the question is adding an RCD minor works. Lots of differing views.
My view is it falls outside minor as a change to the fixed wiring and normally related to the distribution board.
But interested to hear views both ways.
Google away it is Minor Works.
 
Interesting to google the question is adding an RCD minor works. Lots of differing views.
My view is it falls outside minor as a change to the fixed wiring and normally related to the distribution board.
But interested to hear views both ways.

Hum..... This post makes it so obvious you aren't working to earn a living as a spark as no spark would advocate filling out an EIC when they could do a single page MWC
 
If it is an existing circuit, then any alteration to it is an alteration.
An EIC may be used or a MEIWC may be used.
If there are a number of circuits being altered then perhaps an EIC would be better as a MEIWC should only be used for a single circuit.
 
Hum..... This post makes it so obvious you aren't working to earn a living as a spark as no spark would advocate filling out an EIC when they could do a single page MWC

You rumbled me Murdoch although reading my profile would have told you the same.
Yup I come from the Broadcast TV industry as an Engineer so Electrics was just part of my work over 30 years. And its a very different world to domestic as we have the time and budget not to need to cut corners.
That was then and I'm now delivering technical training a few days a month with pays the wages. The move to Domestic work was partly based on local demand and partly as an alternative local part time job (the technical training often involves travel and hotels) So my training and recent C&G exams are still fresh in my mind which is why its so interesting to hear opinions on these forums so different to what's being taught nowadays.

Maybe they teach at a "stricter" level on the assumption that exposer in the field will level the actual delivery? Who knows.

But yes I do have the luxury of only tackling the jobs I feel comfortable with and applying the regulations as I've been taught. If I'm losing work then others are gaining which is fine by me.

Apologies for the off topic wandering.
 
Y
Yup I come from the Broadcast TV industry as an Engineer so Electrics was just part of my work over 30 years. And its a very different world to domestic as we have the time and budget not to need to cut corners.

Hum... a MWC is perfectly acceptable - how is that cutting corners?
 
Because I was explicitly told it wasn't. So to do so would be to go against what I was taught.
But I'm sure time will wear of my new corners.
 

Reply to Minor works certified with no RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
983
In 2019, I had a lot of renovation work done including a full re-wire of our three storey house. Before the re-wire was finished, we parted...
Replies
6
Views
605
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
850
Evening all, Pretty straightforward I think. I was led to believe that surge protection needs to be fitted on all additions and alterations...
Replies
15
Views
4K
Hi Everyone, This is my last question/post for tonight, promise. Please can I ask for a little advice on certificates as I am now questioning...
Replies
4
Views
949

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock