If it's a hard fault like a screw penetration, you can find it without any opening or splitting. Ensure everything is disconnected, separate the ends at the DB and connect a small regulated current source, say 1A, across the faulted cores of one end only. Go round the points reading the voltage across these cores. As you move towards the fault from the energised end the voltage will drop, when you reach the fault it will be near zero and all points beyond it will be identical.
In effect you are doing manually what a continuity tester does, but because you are using a four-lead connection to the fault (current injected through the circuit conductors, voltage read via the outlet) you eliminate the relatively high and variable contact resistance and get a much more precise indication.
If the CPC isn't picking up any parallel paths, the drop for 1A will be about 20mV per metre of 2.5 T+E, so with an ordinary DMM that will read in mV, you can localise to within a few inches.
Alternatively, if you pump in an audio frequency tone, provided the wiring is not in metallic containment you can find the fault with a search coil, if it happens to be buried in the wall rather than at a point. Standard practice in comms wiring.