Discuss Most effective or correct way to fault find? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

If it's a hard fault like a screw penetration, you can find it without any opening or splitting. Ensure everything is disconnected, separate the ends at the DB and connect a small regulated current source, say 1A, across the faulted cores of one end only. Go round the points reading the voltage across these cores. As you move towards the fault from the energised end the voltage will drop, when you reach the fault it will be near zero and all points beyond it will be identical.

In effect you are doing manually what a continuity tester does, but because you are using a four-lead connection to the fault (current injected through the circuit conductors, voltage read via the outlet) you eliminate the relatively high and variable contact resistance and get a much more precise indication.

If the CPC isn't picking up any parallel paths, the drop for 1A will be about 20mV per metre of 2.5 T+E, so with an ordinary DMM that will read in mV, you can localise to within a few inches.

Alternatively, if you pump in an audio frequency tone, provided the wiring is not in metallic containment you can find the fault with a search coil, if it happens to be buried in the wall rather than at a point. Standard practice in comms wiring.
 
Now there's a good idea !
And constant current sources are pretty commonly available these days in the form of LED drivers. Might have to use 750 mA rather than 1A but that shouldn't make a huge difference I wouldn't have thought?

Or just knock up a 1A supply with a LM317 or similar
 
Precisely. Unfortunately you can't just use a modern SMPSU and put it into current limit as it will fold back to next to nothing or go into burst mode.

Of course, if the fault is much more than an ohm or so it will tend to get lost amongst the cable resistance unless the circuit is very long, making it harder to locate. Also, if the test supply has much voltage compliance, you could dissipate significant heat and make the fault worse. Limiting it to a couple of volts is a good idea, or use a lower current like 100mA if you don't need pinpoint accuracy.
 
If it's a hard fault like a screw penetration, you can find it without any opening or splitting. Ensure everything is disconnected, separate the ends at the DB and connect a small regulated current source, say 1A, across the faulted cores of one end only. Go round the points reading the voltage across these cores. As you move towards the fault from the energised end the voltage will drop, when you reach the fault it will be near zero and all points beyond it will be identical.

In effect you are doing manually what a continuity tester does, but because you are using a four-lead connection to the fault (current injected through the circuit conductors, voltage read via the outlet) you eliminate the relatively high and variable contact resistance and get a much more precise indication.

If the CPC isn't picking up any parallel paths, the drop for 1A will be about 20mV per metre of 2.5 T+E, so with an ordinary DMM that will read in mV, you can localise to within a few inches.

Alternatively, if you pump in an audio frequency tone, provided the wiring is not in metallic containment you can find the fault with a search coil, if it happens to be buried in the wall rather than at a point. Standard practice in comms wiring.
I have an older type BT Tone Generator,that i have played with,although i have to admit,not having actually diagnosing a fault using it. It is in a box with some Yankee gear that we experimented with years ago,in an attempt to apply a traceable signal to an underground water main. If i remember,its' success rated alongside that of a capable divining rod exponent...:conehead:
 
I recently did an EICR on a small 3 bed property where it had been DIY rewired at some point.

The socket rings were a bit awkward to fault find.

1 socket in lounge, 1 in kitchen, 1 in bed 1, 1 in bed 2 ...


Next ring similar.

Lighting similar.

Immersion cct also fed a socket in living room and 1 in kitchen.

You get the picture.

A nightmare to map out never mind fault find.

In the end my best friends were pen, paper and patience.
 
Before answering this, i want more info, such as How has the fault come to light, what are the symptoms, and what are the protective device arrangements. I would then decide how to find the fault.

A recent example i had.

Lighting circuit trips RCD when any light on circuit is switched on, no fault with lights switched off, it has a 6a mCB and 30mA RCD. It is wired in 1.5mm T&E, and is brand new rewired circuit loop in/out. So straight away i know switch wires are OK, so i IR each leg of the loop and find that bed 3 to bathroom loop has 0 meg N-E, Replaced cable job done.

Cheers.............Howard
 
Before answering this, i want more info, such as How has the fault come to light, what are the symptoms, and what are the protective device arrangements. I would then decide how to find the fault.

A recent example i had.

Lighting circuit trips RCD when any light on circuit is switched on, no fault with lights switched off, it has a 6a mCB and 30mA RCD. It is wired in 1.5mm T&E, and is brand new rewired circuit loop in/out. So straight away i know switch wires are OK, so i IR each leg of the loop and find that bed 3 to bathroom loop has 0 meg N-E, Replaced cable job done.

Cheers.............Howard

That's bad on a newly wired circuit. What had happened to the cable on the Bedroom to Bathroom Leg to give to N-E fault?
 
That's bad on a newly wired circuit. What had happened to the cable on the Bedroom to Bathroom Leg to give to N-E fault?
Not sure if any of you guys have come across this, but a few years back while doing a rewire during the final test we found a similar fault. It turned out to be a length of faulty t&e. I took the cable back to the suppliers as it was a manufacturing fault.
 

Reply to Most effective or correct way to fault find? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
500
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
903
Hi! DIYer here. I have an MCB running to a cooker isolator switch. The RCD connected to this set of MCBs is tripping and isolating the cooker MCB...
Replies
4
Views
777
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
500

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock