Hello there

I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of warranty!

None of the wiring set up has changed other than a new AC plug for the Solis inverter. I have a 16-panel 4kw system.

It seems, when the inverter 'wakes' in the morning it trips the main house electrics RCD/consumer unit. The solar system is running through a 20amp RCD on the consumer unit and as I say, this is how it was originally installed (and worked well until the Sungrow failure!). I have replaced the RCD just in case that was the issue but it still trips at start-up.

Any suggestions please?

One thing I'm not clear on (install instructions vague?) is: should I run a separate EARTH cable from the AC side isolator switch to the Solis inverter's case? Could not having this be causing the daily trip?

Thanks
 
Can you post up a pic of your CU?

Is the solar on a shared RCD board. What is actually tripping? Main RCD?

Thanks

Norton
Hi Norton, the middle RCD/main protected circuits keeps tripping at start-up. Hope that helps? Thanks.
 

Attachments

  • IMG_0932.JPG
    429.7 KB · Views: 23
Can you post up a pic of your CU?

Is the solar on a shared RCD board. What is actually tripping? Main RCD?

Thanks

Norton
...the solar has been wired into a spare within the protected circuits area so ends up tripping the house sockets, cooker, shower etc that are on the protected RCD?
 
Dangerous as well. If an earth fault occurred, such as you making contact with live mains, the RCD should disconnect the power in a sufficiently short time to prevent you from being electrocuted. The RCD will switch off as intended, but power will still be being supplied by the PV array, until it detects the loss of mains power and shuts down as well. This time will be far greater than the time it takes to electrocute you.
 

Reply to New Solis inverter trips house electrics in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi folks, I have recently had a 5kW Solis inverter and 15kW/hr of batteries installed. Everything is working fine, but I have some concerns about...
Replies
3
Views
403
Hi all, My 3 month old grid tie inverter has tripped on 3 occasions at startup. Have read plenty of threads here about similar issues but unclear...
Replies
1
Views
2K
Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
724
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
I have a 4kw system and a Solic 200 installed - all good since installation. I had a Solis inverter and Pylontech battery installed, but the Solic...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock