Search the forum,

Discuss no earth in the UK Electrical Forum area at ElectriciansForums.net

Bring it on! Can anyone advise me on staying with the thread, I keep having to leave then return to view updates or make comments, cheers.
 
an instructor who i did the 2391 with told me about the time he used to work at sharlston pit..
he said they had been trying for years to get a stable earth....
there was an old tractor engine block in a field out the back of the pit....they found that no matter what the weather was like the Ra was stable on this....so thats what they ended up using as the main earthing `spike`....
he said they used it right until the pit closed.....
 
Absolute, how many times have you had an Ra reading of 150 or more and then carried out the same test on the incoming water main and found a reading of 20 etc, Im not saying you can use a water main as a stable earth you cant(plastic pipes etc) but if its sound and reliable then bobs your teapot.
 
:oops: I've started the countdown timer ...........


Hkq3c.gif

Cracked the popcorn out
 
Oh yes, but very often right so put your tin hat on haha

He's right most of the time, there's no doubt he knows what he's talking about!, comes to something when it's pretty much only Tony that can successfully correct him!.

Right you have all been warned about mentioning TT systems when there's a chance E54 will jump out the coffin that he's kept in, all we need now is for someone to throw exporting a PME into the equation and he will be straight on his soap box!!.
 
What is that?

Well back in the old days before everything was individually wrapped in plastic, soap used to be delivered to the shops in wooden boxes. These were called soap boxes, and folk who thought they had something to say to other folk would stand on them to gain a bit of height while they were saying what they wanted to say. Often used at Speakers' Corner in Hyde Park (that's in London I believe) :)
 
Absolute, how many times have you had an Ra reading of 150 or more and then carried out the same test on the incoming water main and found a reading of 20 etc, Im not saying you can use a water main as a stable earth you cant(plastic pipes etc) but if its sound and reliable then bobs your teapot.
place i was at a bit back....
recent panel...new colours so since 2005...but whoever had done it decided to use the lead water incoming as the means of earthing...
Ze=0.37
it wasn`t a case of leave as is indefinately....i explained to the client that the earthing arrangements needed upgrading...and arranged a PME connection for them at their request...
at least at 0.37 i was happy to leave as is until the DNO had been out....
 
an instructor who i did the 2391 with told me about the time he used to work at sharlston pit..
he said they had been trying for years to get a stable earth....
there was an old tractor engine block in a field out the back of the pit....they found that no matter what the weather was like the Ra was stable on this....so thats what they ended up using as the main earthing `spike`....
he said they used it right until the pit closed.....

I thought they used an IT system in the mines, hardly an earth at all?
 
Ofcourse, as a temp measure a water main is much more reliable than dodgy reading Ra on an electrode, however it could be replaced with plastic, so any pemenent matalic stucture that is soundly connected to earth and in your opinion doesnt deteriorate is acceptable as a reliable earth in aTT system.
 
Ofcourse, as a temp measure a water main is much more reliable than dodgy reading Ra on an electrode, however it could be replaced with plastic, so any pemenent matalic stucture that is soundly connected to earth and in your opinion doesnt deteriorate is acceptable as a reliable earth in aTT system.
indeed but given that the DNO were going to be out in about 2 weeks from the time i called the duty engineer i was happy to leave as is...
we were on site every day so if there had been any diggery pokery going on with the water supplies out on the street we would`v known about it...and would`v acted accordingly (temp rod/s)
 
The only thing is though if you can't get back for some reason, you have left a code 2 departure and your arse wouldn't touch in the (unlikely) event of a loss. Just make sure your scheme provider doesn't get a complaint about it or see it.
 
The only thing is though if you can't get back for some reason, you have left a code 2 departure and your arse wouldn't touch in the (unlikely) event of a loss. Just make sure your scheme provider doesn't get a complaint about it or see it.
no...its been done (PMEd)...like i says at #65
and i`m not in the habit of leaving 2s either...lol....
 
Just a note for engineer 54, it doesnt half to be an earth rod to make it TT,any permenently fixed earth source will suffice.

So long as it meets the requirements of an electrical permanent electrode you'd be right. Such a suitable electrode would be for instance a Ufer earth, or say a steel building where the steel posts have been driven or concreted into the ground.

What isn't acceptable, is the use of extraneous service pipes that can be replaced by plastic service pipe at any time. It is also not generally permissable to use metallic service pipes, as the sole means of earthing to an electrical installation. So even in this case, it cannot be deemed a TT system!!
 
Aye ye are ................... for a Tyke ;)
i mean it would of course depend on the individual scenareo...
now, if we hadn`t been on that site every day for the time it took for the DNO to sort out a PME...i would of course not left it like it was..
but the first thing i did before anything else was get a Ze ..just to confirm there was actually an earth at the property (church)...and as i found it to be suitably low...i made the concious decision to leave it as is until the PME was done...
now if it was a case of just being there for ...say a couple of days..well, theres a different matter completely and a temporary rod would have been installed
 
i mean it would of course depend on the individual scenareo...
now, if we hadn`t been on that site every day for the time it took for the DNO to sort out a PME...i would of course not left it like it was..
but the first thing i did before anything else was get a Ze ..just to confirm there was actually an earth at the property (church)...and as i found it to be suitably low...i made the concious decision to leave it as is until the PME was done...
now if it was a case of just being there for ...say a couple of days..well, theres a different matter completely and a temporary rod would have been installed


Yes, of course Glen .... we believe you !! :wink_smile:
 
When I tested my home installation a few weeks ago out of curiousity I found the Ra to be fairly pants (by which I mean 'not good', not a pair of pants buried and connected to the earthing conductor, like GlennSparks tractor engine) around 120 ohms, but with all the bonding (gas and water) and the bent copper pipe with an earth connected to it, I got 0.something ohms instead. I know technically I should try to get the twig itself a bit better, but with a reading like that I'm not sure I'll bother! One day I will test the bent copper pipe that is hammered into the ground under the house on its own and see what reading that gives.
 
Your down to less than an ohm on your bonded pipe work?? lol!! Sorry i find that extremely hard to believe, in fact i'll go as far as saying, i don't believe it!!!!!!! So why is your earth rod only giving you an Ra of 120 ohms??
 
Just a bit of information picked up today, just finished a new build in the middle of nowhere and had supplier out to provide new supply, all overheads so presumed I would need earth rods, all installed ready, engineer turned up dropped an earth loop on and stuck a cut out with earth terminal, when questioned on this he said as long as they get a reading less than 0.4 ohms they automatically put a cut out with earth terminal. Not sure if this is everywhere or just regional. Waste of earth rods and time but will know better next time.
 
Just a bit of information picked up today, just finished a new build in the middle of nowhere and had supplier out to provide new supply, all overheads so presumed I would need earth rods, all installed ready, engineer turned up dropped an earth loop on and stuck a cut out with earth terminal, when questioned on this he said as long as they get a reading less than 0.4 ohms they automatically put a cut out with earth terminal. Not sure if this is everywhere or just regional. Waste of earth rods and time but will know better next time.

Wrong!! it was a very worthwhile, and certainly not a waste of time on your part!! It is always a good idea to have a local earth rod on a PME earth connection, especially if it's around the 20 ohms mark!! Many European countries insist on a local earth rod at all PME supplied installations!!
 
Wrong!! it was a very worthwhile, and certainly not a waste of time on your part!! It is always a good idea to have a local earth rod on a PME earth connection, especially if it's around the 20 ohms mark!! Many European countries insist on a local earth rod at all PME supplied installations!!
yep...better than just relying on extranious should the neutral go floating...
 
When I tested my home installation a few weeks ago out of curiousity I found the Ra to be fairly pants (by which I mean 'not good', not a pair of pants buried and connected to the earthing conductor, like GlennSparks tractor engine) around 120 ohms, but with all the bonding (gas and water) and the bent copper pipe with an earth connected to it, I got 0.something ohms instead. I know technically I should try to get the twig itself a bit better, but with a reading like that I'm not sure I'll bother! One day I will test the bent copper pipe that is hammered into the ground under the house on its own and see what reading that gives.

I needed a temporary rod and used a scrap bit of 15mm copper pipe about 4 feet long which I hammered into the lawn. I was quite surprised to get an Ra of 80 Ohms without really trying. I was expecting it to be higher.
 
Your down to less than an ohm on your bonded pipe work?? lol!! Sorry i find that extremely hard to believe, in fact i'll go as far as saying, i don't believe it!!!!!!! So why is your earth rod only giving you an Ra of 120 ohms??
Hmm, maybe I'm doing something wrong. As I'm at a bit of a loose end this morning I think I'll have another go.
 
Your down to less than an ohm on your bonded pipe work?? lol!! Sorry i find that extremely hard to believe, in fact i'll go as far as saying, i don't believe it!!!!!!! So why is your earth rod only giving you an Ra of 120 ohms??
Ok, just done another test, and here are my results. Please tell me if I am doing something wrong.

Measuring Loop impedence L->PE with my probes on the tails going into the RCD for L and N, and the PE croc clip on the rod's earth cable disconnected from the MET I get 134 ohms. I put this bad reading down to it being an ancient thin twig you I can easily pull in and out of the ground by hand, and what looks like a very old 4mm earth conductor.

Measuring as above with the PE croc clip on the bond cable (which remember also has the buried copper pipe on it), I get 0.35 ohms (PFC 574A). I put this down to the copper in the hard clay earth underneath the house, metal gas pipe buried in the earth, and the fact that I am about 200 metres from the transformer. (just walked to the transformer and it is 173 paces with my little dwarf-legs :))
 
Last edited by a moderator:
Its a long thread to read the full story
You have a high reading on your rod and have metal service pipes which gives a low Zs when connected

I know you say the transformer is nearby,is next door Pme ?
 
Thanks for the confirmation, that's what I thought. I'm fairly sure none of my neighbours are PME - certainly one side isn't as I've seen the installation.

I've sort of hijacked this thread. My story starts with this: http://www.electriciansforums.net/e...trical-forum/75022-no-earth-5.html#post751011

To which Eng54 replied:
Your down to less than an ohm on your bonded pipe work?? lol!! Sorry i find that extremely hard to believe, in fact i'll go as far as saying, i don't believe it!!!!!!! So why is your earth rod only giving you an Ra of 120 ohms??
 
Ok, just done another test, and here are my results. Please tell me if I am doing something wrong.

Measuring Loop impedence L->PE with my probes on the tails going into the RCD for L and N, and the PE croc clip on the rod's earth cable disconnected from the MET I get 134 ohms. I put this bad reading down to it being an ancient thin twig you I can easily pull in and out of the ground by hand, and what looks like a very old 4mm earth conductor.

Measuring as above with the PE croc clip on the bond cable (which remember also has the buried copper pipe on it), I get 0.35 ohms (PFC 574A). I put this down to the copper in the hard clay earth underneath the house, metal gas pipe buried in the earth, and the fact that I am about 200 metres from the transformer. (just walked to the transformer and it is 173 paces with my little dwarf-legs :))

Metal service pipes are not laid into the ground bare, they will have some form of protective wrapping/coating on them to prevent premature corrosion!! Unless there is some sort of bonding connection from the DNO's Transformer (which is possible but unlikely) there would be little chance of seeing such a low value. Or as has been suggested, a neighbour has had their installation PME'd (legally or illegally) and your picking up their bonded metal pipework Check with the DNO, if a PME connection is available to you!! ...

Have you tried Loop testing the individual incoming service pipes to see what they are giving you? or loop testing the MET without the earth rod connected?? lol!!
 
Last edited by a moderator:
Its a long thread to read the full story
You have a high reading on your rod and have metal service pipes which gives a low Zs when connected

I know you say the transformer is nearby,is next door Pme ?
hmm...well lets face it des...he should know that relying on extranious to bring down external loop isn`t on is it
we know this happens due to parallell paths but he should know the whole idea of doing a Ze in the first place...
if he cant fathom that one...then he`s no business testing ...has he...
 
My gas pipe is definitely straight in the ground, as I can see it - its an ancient iron/steel thing that disappears into the earth. Anyway, I disconnected the bond from the gas pipe and still got 0.46, but then it ocurred to me: as the pipe is connected to appliances which have their metalwork earthed, am I not getting a parallel path through their CPC's? I'm not going to the trouble of disconnecting those, or the bonds on the water pipe or central heating as they are under the floor and a pain in the arse to get to. I'm getting more confused about this by the minute!

The more I think about it I think it is the gas service, as (a) it is a metal pipe going straight into the ground, and (b) the gas-main in the road goes right past the transformer within about 2 metres of it.

Testing the MET without the twig got me 0.35.
 
My gas pipe is definitely straight in the ground, as I can see it - its an ancient iron/steel thing that disappears into the earth. Anyway, I disconnected the bond from the gas pipe and still got 0.46, but then it ocurred to me: as the pipe is connected to appliances which have their metalwork earthed, am I not getting a parallel path through their CPC's? I'm not going to the trouble of disconnecting those, or the bonds on the water pipe or central heating as they are under the floor and a pain in the arse to get to. I'm getting more confused about this by the minute!

The more I think about it I think it is the gas service, as (a) it is a metal pipe going straight into the ground, and (b) the gas-main in the road goes right past the transformer within about 2 metres of it.

Testing the MET without the twig got me 0.35.
stroppy...what is it exactly your trying to acheave here mate?
verify there either is..or isn`t an earth at the property?...if this is the case then you need to be discounting extranious paths....and you know how to be doing that...dont you...
 
hmm...well lets face it des...he should know that relying on extranious to bring down external loop isn`t on is it
we know this happens due to parallell paths but he should know the whole idea of doing a Ze in the first place...
if he cant fathom that one...then he`s no business testing ...has he...
I'm not relying on it, I and E54 are just curious as to how it manages to be so low, and yes I know about parallel paths and the purpose of Ze thank you.

As for can't fathom and no business testing, I presume you knew all about Zs Ze Ra parallel paths and testing as soon as you popped out of the womb, did you? No, you learnt it, which is what I'm doing.
 
What I'm trying to achieve is work out how my Ze is so low when E54 thinks it is impossible. It all started out of curiousity about my earth stake, which I knew would be rubbish so intend to upgrade it, unless I can get myself PME'd. And yes I've discounted the ext paths, leaving me with my 134 ohm earth stake as my 'official' earth path.

I suppose I've confused things by discussing this in a thread called "no earth." I should have started another thread "earth too good to be true!"
 
Last edited by a moderator:
Stroppy, if you're that close to your local tranny, fit an MET in your house, then run a 16mm cable from it to said transformer and bolt your cable onto it. Cover it over with dead leaves and other general detritus.
Should give you the best Ze in the area.
 
I'm not relying on it, I and E54 are just curious as to how it manages to be so low, and yes I know about parallel paths and the purpose of Ze thank you.

As for can't fathom and no business testing, I presume you knew all about Zs Ze Ra parallel paths and testing as soon as you popped out of the womb, did you? No, you learnt it, which is what I'm doing.
how did you guess?...the cable ends were a bit scratchy mind on the way out but...
well, thats what i was told anyway....
 

Reply to no earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
579
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock