Discuss no earth in the UK Electrical Forum area at ElectriciansForums.net

You should not be talking to the sales line. Press whichever button gets you through to the power cut dept, and from there you should be able to talk to someone regarding getting an engineer out within 48 hrs to sort the earthing out. I find it strange that there is no sign of an earth at all, past or present...

It's quite common here in Geordieland.

A lot of my work was in Tyneside flats which were built about 1910 and were originally lit by gas with electricity being installed later (1920 onwards I think)

Houses built in the 1920s were supplied with electricity as they were built. Neither these houses nor the flats had any form of earth supplied other than via the water incomer.
 
Thanks to all, iv installed .any rods and more than comfortable with that, as someome else i found it strange their was no form of earthing at all, thats whats threw me as iv never came across a property without a system already in weather it be tncs tns or tt
 
Just to throw another spanner in the works, you mention it's a very old property, are the suppliers cable lead sheathed (pilc) they used to sweat an earth on to the lead sheath as an earth. These tend to break off over time with years of abuse. If so get on to supply company for upgrade, think its a free service, although I may be wrong.
 
Just to throw another spanner in the works, you mention it's a very old property, are the suppliers cable lead sheathed (pilc) they used to sweat an earth on to the lead sheath as an earth. These tend to break off over time with years of abuse. If so get on to supply company for upgrade, think its a free service, although I may be wrong.
and trying to get them to come out if the sheath earth has come off?...they will just say `it aint distributer earth`....and as such will just tell you to rod it....
any excuse not to come out...
 
I don't quite understand why people are saying that the existing earthing system is a TT system?? If it doesn't have an earth electrode, then it can't be a TT system. It's just an installation that doesn't have any earthing provided!!
 
or alternatively you could do it right...

get 3X 5/8" rods 2 connectors and a striking top...

dig a hole where you intend to site the rod (about a meter away from the building so as not to intercept any foundation/building rubble)...you dig the hole where you intend to site the rod to ensure there are no buried services there....
once you have verified its safe to drive rods down...start doing so...once the first rod is in connect the second rod onto the first and carry on driving it in...
once the second rod is in get a test on it....
you may not need the third rod...if not then the wholesalers should accept it back as long as it hasn`t been used/damaged....

If its a back to back around Armley, doing it "right" might not be an option and certainly not profitable for a rewire quote.
 
I don't quite understand why people are saying that the existing earthing system is a TT system?? If it doesn't have an earth electrode, then it can't be a TT system. It's just an installation that doesn't have any earthing provided!!
It has to be treat like one to illiminate the code 2 departure to allow an addition or alteration.
 
It has to be treat like one to illiminate the code 2 departure to allow an addition or alteration.


Pardon?? If there isn't a made electrode connected to the installation, then it's not a TT system, it's that simple!!

The OP's best bet, is to contact the area's DNO and ask if a PME connection is available on the distribution cable supplying this house.
 
Last edited by a moderator:
Pardon?? If there isn't a made electrode connected to the installation, then it's not a TT system, it's that simple!!

The OP's best bet, is to contact the area's DNO and ask if a PME connection is available on the distribution cable supplying this house.
Can you tell me what defines a TT system please? And what is wrong with inserting one or more spikes in the ground to create or improve the earthing arrangement, for pre testing or design for a permanent earthing atrangement?
 
Hi, been to look at a rewire today and no earth connection at all. Tried to contact supply company to enquire weather the property is connected to a pme system but no joy after holding most the afternoon. I presume supply company doesnt have to supply an earth but just wondering if they would upgrade to pme or not? Or possibly it is a pme system but earth has been disconnected at some point (no sign of pme label tho) any views appreciated. Thanks.

Hi. I had the same problem. Went to upgrade the cu at my new house currently and the was no earth. No connected or visible earth rod and no pme.
I called southern electric on the distribution number and they forwarded me to the electrical emergency department.

They booked a pme enquiry but said there would be a charge after they establist it could be done. When the guys from the board came round they did a Ze, got 0.18 ohms. Threw a 16mm in to their neutral and gave me an MET and a length of 16mm to connect the new cu. No charge. Didnt even want a cuppa.

Couldn't have asked for a better result.
 
Can you tell me what defines a TT system please? And what is wrong with inserting one or more spikes in the ground to create or improve the earthing arrangement, for pre testing or design for a permanent earthing atrangement?


Nothing wrong in inserting one or more rods/spikes in the ground to create or improve any earthing arrangement, be it TN-S or TNC-S or even to improve an existing TT system etc!! In electrical earthing terms, a TT system needs an earth electrode. As the OP has stated that no earthing is present at this installation, and no mention of bonding connections to service pipes (not that i would call that a TT system either, which is also not permissible )etc, then it ain't a TT system is it??
 
Pardon?? If there isn't a made electrode connected to the installation, then it's not a TT system, it's that simple!!

The OP's best bet, is to contact the area's DNO and ask if a PME connection is available on the distribution cable supplying this house.

Totally agree, and can't see the issue here. When I find installations with bad earth connections, UKPN treat it as an emergency, and if they can't get out straight away, they'll certainly be out within 48 hours.
 
If its a back to back around Armley, doing it "right" might not be an option and certainly not profitable for a rewire quote.
well for a start...you`l find that a lot of `em in back to back areas like armley, harehills etc are TN-S....theres often evidence though of the old earth rod in the cellars...

be aware as well that quite a few of `em (not all) but quite a few are high....
 
well for a start...you`l find that a lot of `em in back to back areas like armley, harehills etc are TN-S....theres often evidence though of the old earth rod in the cellars...

be aware as well that quite a few of `em (not all) but quite a few are high....

Is that because of what is growing in the cellars?? :)
 
Can't be spotted by the helicopters!
well Archy...
i have it on good information the current trend for growers is to erect a kind of `tent` in the loft...this shields any horticultural activities from `prying eyes`..

i also have it on good information that the current trend for growers is erm...well, nicking current....
 

Reply to no earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
535
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock