Discuss no earth in the UK Electrical Forum area at ElectriciansForums.net

dig the garden then

Its going to down about metre so unless you're putting in the foundations for an extension then its unlikely to be affected. A loop measurement or better still, run your test electrodes across the lawn and into the next doors garden to get a resistance would be sufficient.

Alternatively use the exploration hole to wack in a 'twigg' and back fill with bentonite - Job done - lol
 
I do realise that the services are not there to be used as an earth, and the difference between earthing and bonding, which is why I started all this: testing the effectiveness of my earth twig. I will see if I can get PME'd, which would be the better option, otherwise I'll get some chunky rods and start driving them into the mud-bath that is my garden.

One day I'll get under the floor and individually test all the pipework and find which one is the culprit, but for now I CBA!

Regular viewers may remember this discussion about my pitiful 125 ohm reading from my earth rod (and unbelievably low Ze through the bonding). I know it is nice to have follow-up on discussions, so let's put this one to bed:

This afternoon I finished work at lunchtime and as, for once, it is not raining I thought I would sort out my earthing before I got cleaned up for the weekend. I have now pulled out my old 'twig' and pounded in two of Sarnia Electrical's finest shiny 3/8" earth rods and connected up my earthing conductor. Now I have a much more reasonable Ze of 44 ohms and a fault current of a whopping 5 amps.

That will do! As my late wife said, deeper is definitely better. :)
 
Two rods screwed together, so 8 feet.

They weren't 3/8'' rods then, if you were able to couple them together!! The 3/8'' things, are the twigs that you can't couple!! lol!!

Go back and test that new rod installation in 6 months time, you'll see almost certainly see an improvement on the present 44 ohms, ..and it will continue to improve for the next 18 months or so, as the soil slowly compacts tightly around the rods....
 
Exactly, I told you that 'twig's were the way to go.

Wack a 1.2m 'twig' in and the the Ra will decrease because of the contact resistance around the electrode.

Better still, back fill with conducting cement and you've increased the contact resistance immediately.

As an aside, it only works when the soil conditions are right and Hong Kong, Gibraltar and most of Norway plus the Himalayas and a couple of places just outside our local pub are not the best places for any 'twig'
 
Exactly, I told you that 'twig's were the way to go.

Wack a 1.2m 'twig' in and the the Ra will decrease because of the contact resistance around the electrode.

Better still, back fill with conducting cement and you've increased the contact resistance immediately.

As an aside, it only works when the soil conditions are right and Hong Kong, Gibraltar and most of Norway plus the Himalayas and a couple of places just outside our local pub are not the best places for any 'twig'

You can sum that up very easily, where twigs are concerned No-where will twigs be any good!!

I wouldn't say Hong Kong is a particularly bad area for creating a TT system, far from it in fact, depends where your trying to create the system. Remember Hong Kong isn't just the Island(s), it also incorporates a section of the mainland too!! lol!!

The earthing on both the Stations and the tunnel overhead rail system, as a whole, was impeccable on the MTR (Mass Transit Railway). I know because i was responsible for large sections of it, along with various much needed CP systems to suit!! ..lol!!
 
Oops my mistake, they are 5/8" not 3/8". These mediaeval measurements confuse me! 10 or 15mm make more sense to me. (see: What we SHOULD have been taught in our senior year of high school - The Oatmeal )

I will try to remember to retest in a few months time, as hopefully the soil around the top rod will have settled a bit. At the moment with all the movement from driving it in it is flapping like a dick in a shirtsleeve.

As an aside, it only works when the soil conditions are right and ...a couple of places just outside our local pub are not the best places for any 'twig'
Oh I don't know, all the wee would keep the soil nice and moist! Although may corrode the rod quite quickly.
 
I will concede that you are referring to a fully integrated system over several miles - hardly 'twig' territory.

The basic two up two down domestic installation with a 'twig' would suffice, IMO, as long as you get a reasonable Ra of less than about 50 Ohms and as you say this value is likely to decrease as the electrode beds in.

In any case, unless you can get the value of Ra below 1 Ohm you'll need supplementary protection Earth fault protection from RCDs
 
Oops my mistake, they are 5/8" not 3/8". These mediaeval measurements confuse me! 10 or 15mm make more sense to me. (see: What we SHOULD have been taught in our senior year of high school - The Oatmeal )

I will try to remember to retest in a few months time, as hopefully the soil around the top rod will have settled a bit. At the moment with all the movement from driving it in it is flapping like a dick in a shirtsleeve.


Oh I don't know, all the wee would keep the soil nice and moist! Although may corrode the rod quite quickly.

Backfilled with rubble with an overlay of concrete and tarmac ? You'd probably need a 10m RSJ pile driven into the ground
 
I will concede that you are referring to a fully integrated system over several miles - hardly 'twig' territory.

The basic two up two down domestic installation with a 'twig' would suffice, IMO, as long as you get a reasonable Ra of less than about 50 Ohms and as you say this value is likely to decrease as the electrode beds in.

In any case, unless you can get the value of Ra below 1 Ohm you'll need supplementary protection Earth fault protection from RCDs

Well for a start i wasn't referring to twigs in my assessment of Hong Kong, just that it isn't a particularly ALL bad area to create TT systems. I don't think i've ever seen a 2 up, 2 down residence in Hong Kong, they are all high/medium rise apartment blocks, or massive residence's of the very rich!! lol!!

Nope, ...it wouldn't, for a kick off there is no-way that a twig will offer any form of a stable TT system to an installation.

Twig electrodes are no good to man or beast, they are little more than the size and thickness of test spikes used for testing Real electrode rods... lol!! I've actually never seen one either, and certainly not in any of the countries i've worked in. Say's a lot for the UK, when you think about it!! lol
 
Oops my mistake, they are 5/8" not 3/8".

I will try to remember to retest in a few months time, as hopefully the soil around the top rod will have settled a bit. At the moment with all the movement from driving it in it is flapping like a dick in a shirtsleeve.

That's why most electricians that do a lot of TT installations use a SDS with either a shop made or home made driving head, to drive rods into the ground, ....and in a fraction of the time it probably took you. ...lol! It also considerably reduces the flapping about of the rod during installation, that you get when using a club hammer or the like!!
 

Reply to no earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
556
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
Hi all, Would like some advice on the below. Context: Rural French domestic installation TT system Earth rod is situated inside the property...
Replies
6
Views
1K
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock