Discuss Non-Harmonized cable in Enclosure in the UK Electrical Forum area at ElectriciansForums.net

D

dellboy13

Hi All

I am currently designing a complete home automation system based around CBUS dimmers and relays. I have now built the enclosures with the dimmers and relays in so I can start programming / testing them. I have going to get a full spark to install the actual cables and connect the lights.
All the CBUS units need breakers feeding them and fuses on their outputs, which I have wired using red and black 1.5mm cables to DIN rail terminators & MCB in the cabinet which are obviously not Harmonized. Is this OK, the spark (when I find one) will do everything external with Harmonized cable!
 
Thanks Charlie, I spoke to the NICEIC this morning and their technical adviser said that it was OK but I have to sleeve each of the cable with Blue or Brown sleeve to indicate use, if I had to do that I might as well rebuild the setup, it would only by 4 or 5 hours work but a pain in the arse to do.
All cables have been individually numbered, what do you think of the install below, should I re-do it or not bother. Fancy a trip down to North Essex to commission it?

IMG_0983.jpg
IMG_0984.jpg
 
If you asked me to do it i would have no problems at all, just an appropriate label on front of the panel, job done


i would not bother sleeving all those cables whats the point, i doubt anyone who lacks the appropriate knowledge would be messing around inside those panels

very neat work by the way!
 
Hi Welchyboy1
The house is just getting out of the ground now, so I will being pinging you a PM in about 5 or 6 months time for a bit of install and commissioning work :smile5:

I had BBC training when I was a junior engineer, so a bit anally retentive on neatness and paperwork :dizzy2:
 
I would be less concerned with the colour of the cables than I would the din rail fuseholder a being exposed when the lid is on. I can't see enough detail in the pic but they don't normally afford the right protection against direct contact. Also what type of fuses are they and what are they there to protect?
What type of cable have you used for building this?

It could have been a lot neater with a bit of panel trunking in there!

Be careful about your choice of electrician, many won't have a clue how to safely test or get meaningful test results on the outgoing cables from such a dimming unit!
 
I would be less concerned with the colour of the cables than I would the din rail fuseholder a being exposed when the lid is on. I can't see enough detail in the pic but they don't normally afford the right protection against direct contact. Also what type of fuses are they and what are they there to protect?
What type of cable have you used for building this?

It could have been a lot neater with a bit of panel trunking in there!

Be careful about your choice of electrician, many won't have a clue how to safely test or get meaningful test results on the outgoing cables from such a dimming unit!

Those fuse carriers look like Wiedmuller terminal fuses, they take standard 20mm fuses, they are normally enclosed inside of the panels, I don't think they are certified for external use.

Agree about the (lack of) trunking. :)
 
They look like a standard pull-out fuse carrier, which exposes live parts when withdrawn, which is easily done without the use of a key or tool.
But what are those fuses there for? Will they discriminate with the incoming MCBs? Will they safely handle the fault current? It doesn't take much fault current to make some 20mm fuses literally explode.

There are many questions I would be asking before doing anything with it if I was asked to install it.
Ventilation, IP rating, type testing?
 
No cables have been run in the building yet as it is approximately 225mm high so far (just out of the ground). I was intending to run 1.5mm Twin and Earth for all the home automation circuits (all limited to 1A).
Basically the Dimmers & Relay need to be feed by a 10A MCB and each output needs to be protected by either a 1A Type C MCB or 1A glass fuse (8 dimmer channels per dimmer unit and 12 relay channels per Relay unit). There is a total of 7 dimmer/relay units with 64 outputs to protect, so I was a cheap skate and went for the cheaper fuse option.

The other reason that I went for the din rail fuse option is that I wanted to keep it really neat, so the idea was to run 4" square trunking down the left hand side, then along the bottom, then the cables from the house for the home automation side enter the cabinet from the bottom and feed straight up to the Din rail termination units and fuses, ie each T&E would go straight up to the termination point set, not having to split and go to 3 different locations in the cabinet. - Bad idea or am I on the right track?

Regarding the fuses raised out of the enclosure, I was going to get the lock kit for that cabinet, so I could easily change a fuse if needed but would be locked from general access. I had to raise the din rail to achieve this, if it is not acceptable I can drop it back down and cover the fuses.

I was going to use slotted trunking in the cabinet but there are 4 cabinet in total, so going through from one to another was going to be a little messy, so I thought I would lace them in neatly instead, again is this a bad idea, should I re-do with trunking?

The reason that I am doing this is to configure the system before hand & test and then allow the entire lot to be moved in to the new build (once up) on the large board and speed up the second fix process.
There is also 2 other smaller boards to make up!
 
They look like a standard pull-out fuse carrier, which exposes live parts when withdrawn, which is easily done without the use of a key or tool.
But what are those fuses there for? Will they discriminate with the incoming MCBs? Will they safely handle the fault current? It doesn't take much fault current to make some 20mm fuses literally explode.

They are a flip out type, but they can detach quite easily the (carrier part), here is a pic, we used loads of these for feeding digi multifunction meters and the like when building panels, they are secondary fuses.
 

Attachments

  • 2101884-40.jpg
    7.2 KB · Views: 155
I think the colour coding within a 'machine' type enclosure would come under a different BS number so the colours do not have to be in accordance with BS7671 as long as they are identified which you have achieved.

so I thought I would lace them in neatly instead, again is this a bad idea, should I re-do with trunking?

I personally wouldn't tie wrap together the neutrals and lives separately, particularly if you are running ac circuits due to electromagnetic inductive effects.

Otherwise, I wish all electricians produced cabinets as neat as yours......
 
I think the colour coding within a 'machine' type enclosure would come under a different BS number so the colours do not have to be in accordance with BS7671 as long as they are identified which you have achieved.

Exactly!, it has buggerall to do with the Niccy what colours are used inside the panel, so long as they are identifiable
 
Exactly!, it has buggerall to do with the Niccy what colours are used inside the panel, so long as they are identifiable

It has a lot to do with the regulations governing panel building, along with the type of cable, IP rating etc etc. Some of these regulations are law, although I don't personally know enough about them to advise on here about it.

From my point of view if I am asked to install something like this I will be looking for CE marking and a declaration of conformity before I fit it.
 
I often make panels without trunking, lacing and looming was part of my apprenticeship so I don't think trunking is necessary and I certainly wouldn't rewire it for trunking. I'm sure the exposed fuse holders are also fine if you put a shock hazard warning and a lock on the door.

Good luck finding someone to commission ;)
 
I never said trunking was necessary, just that it could have been neater with it. I completely agree it could also have been neater with lacing or cable ties.
 
It has a lot to do with the regulations governing panel building, along with the type of cable, IP rating etc etc. Some of these regulations are law, although I don't personally know enough about them to advise on here about it.
.

The IP ratings are almost (if not exactly) the same as BS7671, namely suitable for the intended environment, minimum IP 4X for the top surface and IP2X for the rest or higher depending on environment.

The colours can be anything except Green, and G/Y this latter only used for CPCs, so long as they are identifiable alpha-numerically.

Inside of the panel is governed by other standards than BS7671, this is also outside the scope of the Nic
 
I wasn't referring to anything you said Dave, the OP asked if he should rewire it for trunking.
 
Thank you all for the advice, I will un-clip the neutrals and lives and keep it tidy with in slotted trunking.

Regarding the fused din rail terminators, do you think a lock on the front door would be adequate or should I push the fuse holders back and cover the slot? When you open the fuse holder, you can see exposed metal which would be live but it is right at the back of the holder, you could not touch it with your finger, only with a screwdriver. The actual ones I used are:-

CN12775-40.jpg
 
Thank you all for the advice, I will un-clip the neutrals and lives and keep it tidy with in slotted trunking.

Regarding the fused din rail terminators, do you think a lock on the front door would be adequate or should I push the fuse holders back and cover the slot? When you open the fuse holder, you can see exposed metal which would be live but it is right at the back of the holder, you could not touch it with your finger, only with a screwdriver. The actual ones I used are:-

CN12775-40.jpg

If the front cover is lockable, or requires a tool to open, you should be fine, I would perhaps have a warning --- Volts label too, although not required in BS7671,most panels I have built do have this label.
 
Sorry I missed the posting from Marvo before posting my last one.

Anybody disagree with the lock idea? I personally think a lock is more secure that the 4 bolts that hold the front on but I know what governing bodies are like!!!

All the gear is either UK Hager or Schneider Electric and purchased from UK wholesalers, so fully UK CE approved. The cabinets are IP40 and installed in a small plant rooms
 

Reply to Non-Harmonized cable in Enclosure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Hi guys, Whilst renewing my loft insulation I came across a few runs of very old cable. (Please see attached pictures). These cables are lead...
Replies
6
Views
2K
Hi Pretty new here, so not sure if this question goes into this thread I am not an electrician; however, I plan to integrate IOT devices and...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock