What earthing system should be used on an off grid install with a solar inverter, wind inverter, battery backup inverter and a 4.5kW floating earth generator?
 
It depends on what the installation is powering.
With a floating earth generator it is hard to arrange a complete installation with anything other than a floating earth, however this is not safe if the installation is extensive.
 
With a floating earth generator it is hard to arrange a complete installation with anything other than a floating earth ...

Hi RB - sorry in advance to ask dumb question - can the floating earth gen be reference to earth by externally connecting one of the floating outputs to gen body and earth stake?
 
You need a solidly earthed point connected to all the supplies that can be used as a permanent earth reference.
You should be looking to get a low resistance earth probably by using wide and deep earthing at multiple points.
The generator would need to be assessed to ensure that it can be solidly referenced to earth on one pole, (yes Wilko it should be possible but the design of the generator must be safe for this to do) it would be best to get an internally earthed generator designed for the purpose.
 
Leaving the generator out of it as it is plugged in and so can be disconnected, the supplies from the inverters don't appear have a reference to earth, I am waiting for a copy of the original cert to see what the installer claimed it to be.
As they are standard inverters presumably on a mains connected system it would rely on the dno for the earth reference, since this has been disconnected there doesn't appear to be one.
 
The inverts are both Aurora Uno
are you sure this is off grid, and not a hybrid system with grid connect and battery back up?

AFAIK those inverters don't have off grid functionality - or is the generator and demand big enough that they're able to take their reference from the generator and just reduce the demand from the generator?
 
I know the tails from the meter go into two neutral blocks and no further:- two uno inverters, an exide battery backup and the said 4.5kW hyundai generator with it's floating earth. also there is a couple of immersion heaters connected directly to the board from the solar/wind.
plus a token 3/8 stake outside the "renewables shed
 
The question still remains what is generating the "grid reference" - what controls the batteries and genny? Sunny Island?
 
The battery supply is a Victron blue power multi plus 5kVA
Quote from manual
"The MultiPlus is provided with a ground relay (relay H, see appendix B) that automatically connects the Neutral output to the chassis if no external AC supply is available"

So it would appear something is not quite right
 

Reply to Off grid earthing system in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
732
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
844
Hi All, I hope you are doing ok. I have a question regarding the 24V system. I am going to build a pergola and I could install 4 panels on it...
Replies
10
Views
652
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
801

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock