What’s the Quickest method of finding exactly where the break in the ring is? It’s on the neutral conductor. Split ring and then join the line and neutral at dB and test between live and neutral at midway on both legs and narrow it down this way?
 
What’s the Quickest method of finding exactly where the break in the ring is? It’s on the neutral conductor. Split ring and then join the line and neutral at dB and test between live and neutral at midway on both legs and narrow it down this way?
Yep best way I know
 
I sometimes do it that way.
Another way, if you are alone in the house, and no-one is watching, and you can unplug everything is to take one end out at the CU and wago each conductor, energise the other end, and then just go around with a socket tester and see what works and doesn't.
If you then do a plug in Zs at the ones that worked, the highest Zs is the closest to the issue.
 
I sometimes do it that way.
Another way, if you are alone in the house, and no-one is watching, and you can unplug everything is to take one end out at the CU and wago each conductor, energise the other end, and then just go around with a socket tester and see what works and doesn't.
If you then do a plug in Zs at the ones that worked, the highest Zs is the closest to the issue.
Or dead test as above but long lead and continuity test from socket adaptor N to one on the N in the DB?
 

Reply to Open circuit fault on ring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
795
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock