Thanks Badged01, I'd nicely reply to your comments like you have but on the iPad so it's not so quick and easy.
Nothing on that circuit works when plugged in due to 0v on L-N
I am confident everything was unplugged and no loads
The breaker didn't trip
The rcd didn't trip
Both were holding fine.
I got an acceptable R1 + R2 at each socket which suggests which suggests line and earth are in those two places, but not the right way round.
If they were the wrong way round, because they had been switched somewhere near the origin lets say, then that would explain why by line to neutral readings were duff as it was really neutral to earth.
I am still confident that they have been switched, I know socket testers ate not the best gadget, but there mus be ome truth it in, isn't there? Like I say I did plug the MFT in to check properly.