Discuss Problem this afternoon in the UK Electrical Forum area at ElectriciansForums.net

Thanks Badged01, I'd nicely reply to your comments like you have but on the iPad so it's not so quick and easy.

Nothing on that circuit works when plugged in due to 0v on L-N

I am confident everything was unplugged and no loads

The breaker didn't trip

The rcd didn't trip

Both were holding fine.

I got an acceptable R1 + R2 at each socket which suggests which suggests line and earth are in those two places, but not the right way round.

If they were the wrong way round, because they had been switched somewhere near the origin lets say, then that would explain why by line to neutral readings were duff as it was really neutral to earth.

I am still confident that they have been switched, I know socket testers ate not the best gadget, but there mus be ome truth it in, isn't there? Like I say I did plug the MFT in to check properly.
 
So you have left the customer without downstairs sockets until Tuesday?? Well your customer won't be enjoying their weekend then, will they!!

Not exactly the best approach for customer care, and i wouldn't blame the customer at all, if he called in another electrician to sort the problem out....

Fault finding on a radial socket circuit is a doddle, a methodical approach would have found the problem within the hour...

He said it had been like it for two days and he had extensions running from upstairs, he was happy to wait, unfortunately for him I am tied up until Tuesday afternoon. It is a doddle usually, but when mr DIY is not telling you the truth it makes things difficult.
 
I am still confident that they have been switched, I know socket testers ate not the best gadget, but there mus be ome truth it in, isn't there? Like I say I did plug the MFT in to check properly.

Not necessarily, ive got a socket tester that regularly reports a missing neutral on perfectly OK sockets, but since I only use for the noise to give an indication of when I've pulled the right fuse i'm not going to replace it any time soon.
 
Well, it was the householder mincing around with the electrics to begin with, so, tough -------! :)

My thoughts entirely, it was commical actually, his mate comes in from over the road who has been helping him this week. He has moved light switches and extended the cables etc, extended the plug circuit with the problem, he did show me the joint which I redid as it was twisted ends with tape...

He had cut the old boiler thermostat off the wall as he said it was for the old boiler and not used so the wire was dead... He buried the cut end in the wall. He showed me where, I said so why is my volt stick (stop laughing) glowing red then when it goes near your dead cable? Pulled it out the other side of the wall, it was live so made safe.

Its a DIY mess, it's probably been like this for a week.
 
And now he is ''Paying'' for a professional to sort his blunders out, except it's not being sorted out is it?? lol!!

It will be sorted, but as it was early Friday evening and had plans, I really didn't want to be there and would rather arrange to look at it properly with more time. He rang me to say he had changed a plug socket and now it's not working, I only went because it sounded like a quick job...
 

Reply to Problem this afternoon in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
748
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
863
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
500
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
300

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top