Discuss Push-in connectors on Leviton outlets in the UK Electrical Forum area at ElectriciansForums.net

dogbob

DIY
Reaction score
6
The electricians who wired my new house (US mainland) used the push-in connections on the back of Leviton budget outlets rather than the screw terminals. I've already had two wiggle loose making the outlets intermittent. They are UL listed outlets, so theoretically, they have been tested for safety and would be fine. Yet, I've got anecdotal evidence (two intermittent connections) that they are not fine.

So I set out to fix the whole house. In most cases, it has been straight-forward. I released the spring tension with a thin blade so the wire pops out, and I reconnect the wire to the adjacent screw.

But in some cases, they used both the push-in and screw terminals to serve as a junction, so I left that terminal untouched.

In my two intermittent cases, the failure didn't arc or catch fire because it was a low power load. I'm worried that someone could run a significant load, like a vacuum cleaner, from one outlet and overheat the junction/connection at another outlet.

Would you recommend that I fix those remaining locations using only the screw terminal and adding a third wire and a wire nut to join the wires together? Is there a better way to fix it? Or am I worried about nothing? Can I assume that if the push-in connection is working now, there's no need to fix it?

I've read that some people don't trust wire nuts, but the only time I've heard of them failing is when they are incorrectly used (wrong size, insufficient stripping, etc.)

Thank you for your advice.
 
This is a UK forum but what I have read on US sites these 'stab' connections are considered wholly unreliable but without physically using them it is difficult to substantiate this. If you are concerned then maybe you are better off pigtailing them to wire nuts, our US member @Megawatt is probably better placed to comment.
 
The electricians who wired my new house (US mainland) used the push-in connections on the back of Leviton budget outlets rather than the screw terminals. I've already had two wiggle loose making the outlets intermittent. They are UL listed outlets, so theoretically, they have been tested for safety and would be fine. Yet, I've got anecdotal evidence (two intermittent connections) that they are not fine.

So I set out to fix the whole house. In most cases, it has been straight-forward. I released the spring tension with a thin blade so the wire pops out, and I reconnect the wire to the adjacent screw.

But in some cases, they used both the push-in and screw terminals to serve as a junction, so I left that terminal untouched.

In my two intermittent cases, the failure didn't arc or catch fire because it was a low power load. I'm worried that someone could run a significant load, like a vacuum cleaner, from one outlet and overheat the junction/connection at another outlet.

Would you recommend that I fix those remaining locations using only the screw terminal and adding a third wire and a wire nut to join the wires together? Is there a better way to fix it? Or am I worried about nothing? Can I assume that if the push-in connection is working now, there's no need to fix it?

I've read that some people don't trust wire nuts, but the only time I've heard of them failing is when they are incorrectly used (wrong size, insufficient stripping, etc.)

Thank you for your advice.
Yes you need to fix all of them. Back stabs are very unreliable and in my opinion shouldn’t even be an option on receptacles. Always use the terminal with the screw. As far as wire nuts they are fine as long as the person who uses them knows how to correctly install them. Wagos are an excellent choice versus wire nuts.
 
Thank you. Yes, I can do that. I'm pretty confident in my abilities with a quality wire nut.

Strange: When I search one of the big-box store's website for Wago, they show Ideal "In-Sure" push-in connectors, which seem like the same stab concept. They may be better than the Leviton stab connector, but it still seems like the same risky concept. I'll pass. In-Sure® Push-In Wire Connector, Model 33 3-Port Orange - https://www.idealind.com/us/en/shop/product-type/connectors/in-surer-push-in-wire-connector-model-33-3-port-orange.html
 

Reply to Push-in connectors on Leviton outlets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
468
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
441
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
892
I have an existing but unused 50A disconnect on the side of the house. It had been connected to an AC unit that got replaced. It has just 3...
Replies
4
Views
936
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock