- Reaction score
- 157
I am undertaking EICR at a sprawling domestic over a house and several barns/guest suites, which is knee deep in C2 and C1 observations.
I have here a ground-mounted PV install without any documentation, not an MCS install, and (I just spoke to DNO), they have no record of it on G59 or G83 and rightly say it needs to be disconnected until then.
It's about 5 KWP, but had little time yet to check further. Two arrays of 10 panels ground mounted South with 2 inverters SRP Australia SR4200TL. Inverters mounted on the frames (which are wood).
TT system, nearest earth stake is about 40M away at the board they feed into via 40A RCBO. (& sub-main to that board itself doesn't meet ADS).
There is no export meter and main meter is disc-style (I suspect the old going-backwards type which may well be it's raison d'être.. but haven't checked).
AC export/supply cables are unprotected blue "Arctic " flex, thrown into the soil and semi/entirely submerged on unknown route. There is a AC isolator on the wall of a barn about 15 M away and thereafter 10mm T&E thrown onto the floor of a barn back to the CU.
No labelling of anything anywhere, no diagrams, no warnings.
Give it to me..
I have here a ground-mounted PV install without any documentation, not an MCS install, and (I just spoke to DNO), they have no record of it on G59 or G83 and rightly say it needs to be disconnected until then.
It's about 5 KWP, but had little time yet to check further. Two arrays of 10 panels ground mounted South with 2 inverters SRP Australia SR4200TL. Inverters mounted on the frames (which are wood).
TT system, nearest earth stake is about 40M away at the board they feed into via 40A RCBO. (& sub-main to that board itself doesn't meet ADS).
There is no export meter and main meter is disc-style (I suspect the old going-backwards type which may well be it's raison d'être.. but haven't checked).
AC export/supply cables are unprotected blue "Arctic " flex, thrown into the soil and semi/entirely submerged on unknown route. There is a AC isolator on the wall of a barn about 15 M away and thereafter 10mm T&E thrown onto the floor of a barn back to the CU.
No labelling of anything anywhere, no diagrams, no warnings.
Give it to me..