hi all
I've got a Rangemaster to install and just want to check my diversity calcs. It's say it's 14.5kw so I make the 63a using diversity I make it 26a or with a socket 31a.

There is a 6mm cable on a 32a mcb, I'm thinking of changing it for 10mm and 40a mcb as its a bit close to max of the 32 mcb.

Just wanting to check my calcs are correct

Thanks
 
your diversity calcs are right. using 240V, i get 25A ans 30A respectively. the 6mm on a 32AMCB is fine as it is. Ib<In<Iz. in actual fact, if the 6mm is ref. method C, you can use a 40A MCB on 6mm. ssssimmmplesss.

edit. leccy in norwich now? i'll be damned/
 
your diversity calcs are right. using 240V, i get 25A ans 30A respectively. the 6mm on a 32AMCB is fine as it is. Ib<In<Iz. in actual fact, if the 6mm is ref. method C, you can use a 40A MCB on 6mm. ssssimmmplesss.

edit. leccy in norwich now? i'll be damned not sure what this means haha

Glad my calcs work out for some reason I was doubt my self think it was because of the 14.5kw figure. This means I haven't got to change anything.
Thanks
 

Reply to Rangemaster diversity calcs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
997
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
630
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock