Discuss RCBO fault finding in the Australia area at ElectriciansForums.net

Just a thought i cant get to involved as outside UK regs for to long. But when someone asks a Q like this instead of just for example putting IR test could we not take the time of how to explain how to and the readings that should be expected could help some of the members that are a bit short on practical experience.

Fair Comment mayfair :Jase31 , the chances are its not an insulation problem this is due to the fact its class 2 very rare to get a problem like that, not impossible mind , when in my first post i point out the tester you needed the PAT tester was to check the appliance reaings IR should be around >200 ohms anythin less than 2 ohms then you could get problems , the RCBO ramp tests should be below 30ma if the RCBO is a 30 ma tripping time ,to find this out you then need an RCD tester this will test the RCBO for correct operation normally the RCBO's will trip around 24ma but i have seen some very over sensitive ones tripping at less than 2ma , so this is what you should be looking for ,you should also test the RCBO tripping times to ,what could cause the problem is leakage of your charger circuits causing an inbalance of the RCBO this could then cause the rcbo to trip , so the tests would reveal that , unfortunatly as i have mentioned in a previouse post you will be unable to carry out these tests with a multi meter , so it maybe an idea to see if you can find some one to either test you charger using a pat tester and even the RCBO to see if thats faulty ,any more advise just ask mate

mayfair if my post sounds as im having ago please be assured im not i 100% agree with your comment so thought i'd add a little more to my original post

Nick
 
Last edited by a moderator:
The charger has a 2 core lead...no cpc.....the only possible place where earth leakage can occur is the plug. Not unknown if the plug is damaged and /or dirty,check it and replace if it looks suspect.
 
Thats the sort of info we should be giving Great post Nick, Its difficult for me to Answer some of these members as I have been in Spain for 21 years and dont want to get someone into trouble.
Fair Comment mayfair :Jase31 , the chances are its not an insulation problem this is due to the fact its class 2 very rare to get a problem like that, not impossible mind , when in my first post i point out the tester you needed the PAT tester was to check the appliance reaings IR should be around >200 ohms anythin less than 2 ohms then you could get problems , the RCBO ramp tests should be below 30ma if the RCBO is a 30 ma tripping time ,to find this out you then need an RCD tester this will test the RCBO for correct operation normally the RCBO's will trip around 24ma but i have seen some very over sensitive ones tripping at less than 2ma , so this is what you should be looking for ,you should also test the RCBO tripping times to ,what could cause the problem is leakage of your charger circuits causing an inbalance of the RCBO this could then cause the rcbo to trip , so the tests would reveal that , unfortunatly as i have mentioned in a previouse post you will be unable to carry out these tests with a multi meter , so it maybe an idea to see if you can find some one to either test you charger using a pat tester and even the RCBO to see if thats faulty ,any more advise just ask mate

mayfair if my post sounds as im having ago please be assured im not i 100% agree with your comment so thought i'd add a little more to my original post

Nick
 
Does the bare charger (minus battery) trip the RCBO? Or does this happen when a battery is plugged in for charging? Have you removed (temporarily) ALL other loads from the circuit protected by the RCBO, whilst attempting to use the charger?
 
A few posts seem to concentrate on the rcbo tripping because of earth leakage,its a class 2 appliance, so it seems very unlikely

Have you considered that the tripping may be the overcurrent part of the Rcbo
Perhaps a few of the primary windings are shorted and its exceeding the rating of the mcb part of the Rcbo
 
instead of jumping on the band wagon of earth leakage faults which as mentioned it is a class 2 equipment so this shouldnt be in the equation he does mention he has an rcbo installed this can also detect an overload too. this happened to me on an ordinary mcb type b. the fault was the battery of the drill have you a spare battery pack to test!!. hope this helps.
 
While it may be a class 2 appliance the plug has an earth pin and if there is dirt/grease in the plug and perhaps a crack or damage to the plug I have known them trip RCD's. Another occasional cause is the cardboard info template that some pugs have on their base when new.....these often get left on and if they get damp enough leakage can occur to trip an RCD....That was the point I made in a previous post,if it is the RCD part tripping it cant be the appliance,it must be the plug......
An overload issue is possible but it seems unlikely that a charger would make much difference,they are only a few watts,unless it is faulty,in which case you would expect it to take out the plug fuse (3a?) rather than a (32a?) mcb.
 
Last edited by a moderator:

Reply to RCBO fault finding in the Australia area at ElectriciansForums.net

Similar Threads

I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
507
Hi I'm trying to find if I have a fault in these to brakers of in the lines. The 32A braker leads as far as I know only to a junction box that use...
Replies
18
Views
1K
Hi all I don't appear to be able to post in the DIY forum so apologies if this is the wrong place. I live in a block of flats with an external...
Replies
3
Views
851
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock