OP
nickblake
Just a thought i cant get to involved as outside UK regs for to long. But when someone asks a Q like this instead of just for example putting IR test could we not take the time of how to explain how to and the readings that should be expected could help some of the members that are a bit short on practical experience.
Fair Comment mayfair :Jase31 , the chances are its not an insulation problem this is due to the fact its class 2 very rare to get a problem like that, not impossible mind , when in my first post i point out the tester you needed the PAT tester was to check the appliance reaings IR should be around >200 ohms anythin less than 2 ohms then you could get problems , the RCBO ramp tests should be below 30ma if the RCBO is a 30 ma tripping time ,to find this out you then need an RCD tester this will test the RCBO for correct operation normally the RCBO's will trip around 24ma but i have seen some very over sensitive ones tripping at less than 2ma , so this is what you should be looking for ,you should also test the RCBO tripping times to ,what could cause the problem is leakage of your charger circuits causing an inbalance of the RCBO this could then cause the rcbo to trip , so the tests would reveal that , unfortunatly as i have mentioned in a previouse post you will be unable to carry out these tests with a multi meter , so it maybe an idea to see if you can find some one to either test you charger using a pat tester and even the RCBO to see if thats faulty ,any more advise just ask mate
mayfair if my post sounds as im having ago please be assured im not i 100% agree with your comment so thought i'd add a little more to my original post
Nick
Last edited by a moderator: