Discuss RCBO's Can the excess wires from them be cut off?? in the Australia area at ElectriciansForums.net

I recently attended a 1st amend seminar given by Hager. One of the chaps was Hagers Tech Manager, so I asked him about this myth. He replied that it's fine to cut the leads to length, but they should be ferruled. I replied thanks and btw why don't you supply a pair of spare ferrules with each RCBO then!!
If I meet him I'd ask him why the 40A RCBO only has a neutral lead suitable for 32A, clearly marked on the lead!
 
Any advice on make for these E54? And should I just get a selection of ferrules?

CK ratchet crimping tools are pretty reasonable for the money. There's no need to go over board, the real expensive crimp tools, are what you would use on aerospace and military type installations, and then they normally provide the crimping tools, which will be tested at regular intervals for compliance....

Most ratchet crimp tools will have an adjustable dial that adjusts final pressure on the ferrule or other crimps....
 
If I meet him I'd ask him why the 40A RCBO only has a neutral lead suitable for 32A, clearly marked on the lead!

I take it your not used to cable ratings in tri rated (fine wire) they usually are alot higher ccc rated like for like with standard stranded cables hence it often looks undersized, but not clear or ever seen a 32amp label on a 40amp breaker its most likely a i.d. error, it just dosn't compute... computer says no! :thumbs_down:
 
Last edited:
I take it your not used to cable ratings in tri rated (fine wire) they usually are alot higher ccc rated like for like with standard stranded cables hence it often looks undersized, but not clear or ever seen a 32amp label on a 40amp breaker its most likely a i.d. error, it just dosn't compute... computer says no! :thumbs_down:

I am not sure that at 50hz fine stranded makes much difference to current handling capacity?

Is it not more related to the shortness of the cable, and the rules of integrated cables not requiring the same 'over rating' that we have to work to with other cables? The environment is more or less fixed, no sheath, no conduit, no thermal insulation, and the safety device is a dead cert!

Skin effect is negligible at 50hz as it is about 8mm deep, and as the strand are not insulated they short out along their length thus negating a lot of any skin effect that may be present. Stranded cable, at small sizes more often takes up more space than solid core of the same CSA due to the unavoidable spaces between the cores.

I hope this was what you meant, otherwise I should have gone to bed.
 
Just spoke to a helpful man on the MK Technical desk and he said:-

1, Shortening the leads is not a problem but recommend a re-ferrule on cable ends.
2, This will not effect warranty of the MK RCBO".
 
Last edited by a moderator:
Lots of excellent info here!

Which crimpers would be best for me? I've seem some which are CK (bootlace ferrule) and then I've seem that are just ferrule crimpers which make a square/rectangular end, but these were £200+ which I'm not prepared to pay!
Would normal crimppers with pin/pointed crimps be ok?
 
That's the sort of money you pay for knipex crimpers, not CK crimpers. Your obviously not looking very far, there are plenty of ratchet crimpers out there for around 20 to 25 quid...
 
Lots of excellent info here!

Which crimpers would be best for me? I've seem some which are CK (bootlace ferrule) and then I've seem that are just ferrule crimpers which make a square/rectangular end, but these were £200+ which I'm not prepared to pay!
Would normal crimppers with pin/pointed crimps be ok?

Try something like these about £20, you dont need anything fancy Buy Tooling - Crimp Terminals TERMINAL CRIMPING TOOL CK 3645 online from RS for next day delivery.
these are just an example but only go up to 2.5mm ferrules, their are plenty of range and options out there if you look.
 
Last edited:

Reply to RCBO's Can the excess wires from them be cut off?? in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Firstly, I hope it is ok to discuss the wiring of speakers here. TBH my ignorance in all things electrical knows no bounds, and I am guessing it...
Replies
31
Views
3K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K
Hey! I bought a few simple on/off switches that you plug into a socket, and they have a single output which is either on or off depending on a...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock