Discuss Recall: Proteus Switchgear - 100 Amp Double Pole Isolator - which might not isolate. in the The Electrical Exchange area at ElectriciansForums.net

Disconnect once check twice..(or more)
Found HERE at Trading Standards
2021-12-17_1021.png

Risk level
Serious

Risk type
Electric shock

Risk description
The fault was identified during routine installation process which includes a test. It was found that the switch did not isolate the circuit. The product does not meet the Electrical Equipment (Safety) Regulations 2016.

Corrective measures
Withdrawal from sale and recall of affected batches by the manufacturer. Recall of the product by the end user, E.ON. E.ON have written to all affected customers to arrange a visit to carry out a safety check of the isolator. E.ON customers who have received a letter to arrange a free visit and have not replied should contact E.ON as soon as possible.
 
Proteus really is cheap crap and living up to it
And you’re basing that on one recall, from one batch, of one product?

Ok. Two batches…. You pedantic bunch.

These things pass their relative BS numbers…. They do the job they are designed for.

So does that mean the standards need to be raised if they’re not good enough?
 
And you’re basing that on one recall, from one batch, of one product?

Ok. Two batches…. You pedantic bunch.

These things pass their relative BS numbers…. They do the job they are designed for.

So does that mean the standards need to be raised if they’re not good enough?

But the recall is because their devices haven't met the required standards in these cases.
 
And they’ve recalled them. As they should.
It’s good to know they have some quality control and act on what they find.

Very true that. Much worse are the companies that know there is a problem with their product but try to avoid a recall.
 
And you’re basing that on one recall, from one batch, of one product?

Ok. Two batches…. You pedantic bunch.

These things pass their relative BS numbers…. They do the job they are designed for.

So does that mean the standards need to be raised if they’re not good enough?
They've been recalled because they don't meet the relative standards
 
And they’ve recalled them. As they should.
It’s good to know they have some quality control and act on what they find.

This may have been identified by the manufacturer, but it's much more likely that Eon noticed a significant rate of failure and contacted the manufacturer. When this type of issue becomes apparent, there is a legal obligation on the manufacturer's part (or importer) to investigate and recall as appropriate. It's not about QC, but about the sort of huge fine that would cripple the manufacturer or importer if they failed to act in accordance with their legal obligations.

Effective QC is what prevents the sort of issue in the first instance. For most companies, that would mean thorough batch testing as such products aren't generally made in the UK. As for manufacturing standards, pretty much everything sold in the UK will meet a particular standard, but some manufacturers like to offer a better product, generally by employing more considerate design and better materials.


Edit: that last sentence is terrible and I don't care 😂
 
it's much more likely that Eon noticed a significant rate of failure and contacted the manufacturer.
I was thinking that too. The circumstances leading to this would be interesting to know.
I'm assuming the issue was detected when fitting new ones as existing ones rarely get tested and Eon wouldn't have occasion to use them much.
I have one in my house and view it with a new suspicion after this report!
 
I was thinking that too. The circumstances leading to this would be interesting to know.
I'm assuming the issue was detected when fitting new ones as existing ones rarely get tested and Eon wouldn't have occasion to use them much.
I have one in my house and view it with a new suspicion after this report!

Pretty certain there's one beside our meter. This thread reminded me about it, but haven't yet mustered enough enthusiasm to check.
 

Reply to Recall: Proteus Switchgear - 100 Amp Double Pole Isolator - which might not isolate. in the The Electrical Exchange area at ElectriciansForums.net

Similar Threads

Saw this on Irish Consumer site (CPCC.ie) HERE Not sure about the rest of the UK but worth checking if you have one. Fluke Europe BV recalls to...
Replies
1
Views
1K
PRODUCT RECALL NOTICE FLUKE 110V VOLTAGE TESTER T110 We have been made aware of some isolated incidents with this product where the voltage tester...
Replies
10
Views
2K
Squid
S
I'm a Facilities Manager and not an electrician though I do have some electrical qualifications of some years ago. I wonder if anyone would like...
Replies
4
Views
8K
R
Got this email today so thought I'd let everyone know incase anyone has fitted one recently Dear Customer, We have identified an issue with the...
Replies
4
Views
2K
M
Product: Electrium Miniature Circuit Breakers (MCBs) Brand: Electrium Type/number of model: The only MCBs affected by this recall are those...
Replies
12
Views
5K
SPARTYKUS
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock