Discuss Ring CPC fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

H

humpa

Hi guys, first time I have posted on the site so looking forward to hearing from you all. I am carrying out a kitchen refit and while testing the ring circuit I have come across a lack of continuity on the CPC circuit. I have carried out testing using the two ends and a R2 wander lead and have managed to track down the break which is situated somewhere between two socket outlets in the study. To test the continuity I temporarily bridged the two earth points n the sockets with a length of 1.5mm earth flex but then obtained the following results :- r1 0.80, rn 0.78, r2 0.30 furthermore the R1+R2 readings average 0.69 for all sockets except the two in the study which read 0.10. With the bridge left in and the circuit energised the average ZS reading was 1.18 with the two linked sockets reading 0.30. Client not keen on me ripping up the house to find the break but beside that I am confused by the readings I have got. Any ideas guys ?
 
Have you identified the leg of the RFC which has the broken cpc?
 
There could be more than i ring coursed by multiple earth connection points caursing parallel earth paths, so in affect you are only testing continuity of a small part of the curcuit try disconnecting both legs of the cpc at at differnt point of the circuit and see if you still have ring continuity
 
Thanks for all the replies guys, don't really want to create two separate radials. Want I don't understand is that I have in affect by bridging the two sockets repaired the broken CPC, but the readings for r2 continuity are far lower than r1 and rn ?
 
Your r1 reading can be low due to supplementary bonding in the property.

r1 is the resistance of the live conductor how will supplementary bonding effect that reading, if it's disconnected from the CU?
 
did you mean r2. bonding will not affect this .

Yeah, I did sorry and If you're testing from a flying lead in the board to a set point remember that the sup' bonding is still on that board and/or "back in the day of JBing every socket" they used to take a single earth to do sup' bondings.
 
Yeah, I did sorry and If you're testing from a flying lead in the board to a set point remember that the sup' bonding is still on that board and/or "back in the day of JBing every socket" they used to take a single earth to do sup' bondings.

Sorry What?
 
if trying to measure R2 with a wander lead from DB to point, then you'd dis the cpc from the board to eliminate any parallel paths.
 
Hi guys, first time I have posted on the site so looking forward to hearing from you all. I am carrying out a kitchen refit and while testing the ring circuit I have come across a lack of continuity on the CPC circuit. I have carried out testing using the two ends and a R2 wander lead and have managed to track down the break which is situated somewhere between two socket outlets in the study. To test the continuity I temporarily bridged the two earth points n the sockets with a length of 1.5mm earth flex but then obtained the following results :- r1 0.80, rn 0.78, r2 0.30 furthermore the R1+R2 readings average 0.69 for all sockets except the two in the study which read 0.10. With the bridge left in and the circuit energised the average ZS reading was 1.18 with the two linked sockets reading 0.30. Client not keen on me ripping up the house to find the break but beside that I am confused by the readings I have got. Any ideas guys ?

http://www.electriciansforums.co.uk...lations/99490-ring-cpc-fault.html#post1067406

This vid tells you how to test a RFC properly
 
55 PP3 s wired in series if you ain't got a megger to hand.
 
i call my lady "google"

1. she's always around.
2. she knows everything
3. she's high maintenance
 
Thanks guys, after giving the problem plenty of thought what I need to do is double check that the break in the CPC is actually were I think it is. Otherwise my piece of bridge cable could be forming a mini ring.
 

Reply to Ring CPC fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
840
Hi! DIYer here. I have an MCB running to a cooker isolator switch. The RCD connected to this set of MCBs is tripping and isolating the cooker MCB...
Replies
4
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock