Discuss Shed wiring ? in the UK Electrical Forum area at ElectriciansForums.net

bemmer2

DIY
Reaction score
0
100 amp box in house and have only 1 open slot for breaker ! I want to wire my new shed with 2-3 led lights and several outlets . Shed is 50’ from house box . Should I install a 30amp + breaker in the open spot and run #10 wire to a small sub panel in the shed or what might work better ? 220 not necessary at this time . Thanks
 
one for Megawatt . most of us are UK based and ain't got a scooby on US regs. and standards. ( with the exception that in the US, if it does not go bang, it's fine ?).
 
100 amp box in house and have only 1 open slot for breaker ! I want to wire my new shed with 2-3 led lights and several outlets . Shed is 50’ from house box . Should I install a 30amp + breaker in the open spot and run #10 wire to a small sub panel in the shed or what might work better ? 220 not necessary at this time . Thanks
Yes you can do that but make sure that the wire is rated for outdoor and direct burial if your not going to install conduit. Make sure the panel you buy is a main lug only and your shed has to be GFCI protected.
 
Yes you can do that but make sure that the wire is rated for outdoor and direct burial if your not going to install conduit. Make sure the panel you buy is a main lug only and your shed has to be GFCI protected.
Thanks ! My choice for box . Yes I will be using conduit to bury and ground fault protected !
 

Attachments

  • 054A7EFD-55C4-458A-9BB3-CF4DB3E111B8.png
    492.5 KB · Views: 14
Yes you can do that but make sure that the wire is rated for outdoor and direct burial if your not going to install conduit. Make sure the panel you buy is a main lug only and your shed has to be GFCI protected.
Thanks ! I think I might have a problem , I ran 10/2 from a new 30amp breaker I installed my house service . I started wiring the shed today and Used the 30 amp box shown . I’m not sure but I think I should have ran 10/3 wire to allow the two breakers to be used ? Is there a way to use the 10/2 already ran and have power to both breakers ? I do not need 220 v at this time .
 

Attachments

  • C7F7B3BC-BCC2-4B92-9AE8-8C0268B44AF8.png
    491.8 KB · Views: 12
Thanks ! I think I might have a problem , I ran 10/2 from a new 30amp breaker I installed my house service . I started wiring the shed today and Used the 30 amp box shown . I’m not sure but I think I should have ran 10/3 wire to allow the two breakers to be used ? Is there a way to use the 10/2 already ran and have power to both breakers ? I do not need 220 v at this time .
Can I jump from 110 feed to other post ?
 

Attachments

  • 0C895B3D-BC81-4973-B556-B51B9003D51C.jpeg
    355.5 KB · Views: 10
Thanks ! I think I might have a problem , I ran 10/2 from a new 30amp breaker I installed my house service . I started wiring the shed today and Used the 30 amp box shown . I’m not sure but I think I should have ran 10/3 wire to allow the two breakers to be used ? Is there a way to use the 10/2 already ran and have power to both breakers ? I do not need 220 v at this time .
You have 2 lugs on top of the panel and right now you only have one wire in it so just install a jumper to the other side. Yes anytime you want to do a project like that, at least pull 3 conductors with a ground
 

Reply to Shed wiring ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
860
I’m planning on putting in a small (10x10) detached shed for garden storage plus a freezer for meat storage, an in-wall AC unit (for temperature...
Replies
9
Views
1K
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
932
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
754
Hello, I had an electrician install a 100Amp subpanel which feeds a mini split. I addition I added a Homeline 50A GFCI breaker to power a shed. I...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock