Discuss Short circuit compliance on high Zs readings in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

cliffed

-
Arms
Supporter
Reaction score
645
Would you divide the 5.13 ohms by 4.
I personally don’t think so.
Also the R1 /Rn short circuit resistances are different from the usual R1 /R2 measurements.
Found those in an electrical book by,that man.
The Zs on this circuitB4707BB1-51E7-4A35-98FA-BA188A64EA04.jpeg was above the permitted figure,so just had a play around to see if this complies,anyone agree.
 
t=K2S2/I2 is the formula to use.
Nothing to do with a high earth fault loop impedance as the line to neutral loop measured loop could be significantly lower.

t being the maximum time in seconds allowed before damage to the live conductors and surrounding insulation occurs.
so does your short circuit fault current disconnect before damage to the live conductors only occur?
 

Reply to Short circuit compliance on high Zs readings in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
798

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock