I have a well pump and motor on it's own meter. I do not have the specs on the motor. It pulls up from about 60' down, at about 45 gpm. And my bill is for about 800 kWh per month. The coop utility power goes out periodically and we want to have a propane generator that I can use to keep my water available and a small milk house heater on when the power goes out. I'm not sure what size to buy. How many watt generator do you think I should buy? Thank you.
 
A 15kva transformer should be fine. I have a well thats 360 feet deep and it has a 5 HP motor in the bottom of the well and it pulls around 7 amps
Thank you.

I have a breaker below the meter. I was going to turn that breaker off, tie in the generator below that breaker, with it's own separate breaker. I would turn off the generator breaker, turn on the main line breaker and go about my business. Then, if the utility power went out, I would go out and turn off the main line breaker, then turn on the generator, and then open the generator breaker to run the well. I would reverse that process when the utility power came back on. If there is something inherently wrong with that proposal, I'm all ears.

Thanks again on the sizing question.
 
The generator and utility feed breaker must be interlocked to meet code. Otherwise by mistake you could feed generator power back into the utility line and electrocute the guy working in the hole in the road. For the generator sizing, you really should try to get some specs on the pump or measure the current.
 
What type of pump is it ? Any chance of a picture of the starter ?
I'm not sure. I've had it replaced several times in the last 21 years. On the second-to-last one, September of 2016, I specifically asked for it to be bumped up since my water right is 45 gpm and I was only pulling 25 gpm. They put in a "Submersible GRUNDFOS Model # 35530-11, 35 gpm, 3450 RPM, 3 HP, 230 Volt, 17 full load amps, intake depth 52', 2" pipe. There has been another one put in since then (about 2 years ago) but I lost the specs on it. It could be the same. I have an email into the guy who did it and he said he'd look, but I haven't heard back. But if we assume the last pump (above) is the same, what do you think?
 

Reply to Sizing a propane standby generator in the USA Electrical Forum area at ElectriciansForums.net

Similar Threads

I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
315
I currently have a 100 amp sub panel for a 50 amp RV hookup (on a 60 amp breaker). This is about 100ft from the main with 2/4 wiring. Would a...
Replies
1
Views
929
Another one that some of you may be interested in.......... We had a call to remove 4 off blackstone generators from a pumping station in south...
Replies
3
Views
1K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
673
Hi all, I've got a small catering business out of a converted horse trailer and purchased an inverter generator to power the trailer, mainly just...
Replies
8
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

USA Electrical Advice

Welcome to the USA Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.

UK Electrical Forum

This is the main UK Electrical Forum at ElectriciansForums.net. Electrician State Laws for Electrics and Electricals may differ on a state-by-state basis. American questions and answers can be found in our UK electrical forum.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top