Search the forum,

Discuss solar cable in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

K

kitaldo

Hi I am building a solar system and need advice on what cable to buy, I bought 6mm2 cable and found the inner wire was only 3mm. I have 4 12volt 80w 5amp panels to be wired in parallel, 2 110amp battery to be wired in parallel. The cable length between panel and batteries is 12m, I have conduit to run cable as it is out in the country.
PS I am new to solar.
 
If you mean that the conductor is about 3mm in diameter, then that does indeed have a cross sectional area of about 6.0mm2 (Pi x d x d )/4. If you're wiring the 4 panels in parallel, then the maximum current you'll get (if 5amp per panel) is circa 20amps and with a low DC voltage ('12V') you'll be dropping about 11% over 12m. The charge controller probably needs 16-22volts to charge a '12V' battery. I.E. if the panels are really 12V it's not going to work, you might for example want the panels with 2 series panels in parallel (nominal 24V at 10amp peak)
 

Reply to solar cable in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I am a retired Electrician and started looking at Solar Power, (Black Magic to me), after much reading of "How To", I decided to build myself a...
Replies
10
Views
1K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
549
I am thinking of having a solar system installed, but am very much a novice, I know that I want solar panels with a battery. So I am looking for...
Replies
0
Views
1K
Afternoon guys, I have a solar installation. The panels and Fox ESS hybrid inverter, Fox Cube batteries, are all installed in the garage. They...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock