Afternoon guys quick question

It’s been a year after the kitchen has been competed and now I’m looking at doing led strip lights under the cabinets on the plynths.

on one side of the kitchen I only have available 2 cooker isolating switches that I wired in for the induction hob and the electric cooker.

My plan is to spur off the outgoing of one of them in 6mm to a single socket immediately below them and plug the led lights it. They are 0.7 Amp zigbee lights.

is this ok? My only worry is an I correctly fusing the spur and would need an extra fused spur between the socket and the cooker switch. I can’t wire the led straight into a fused spur because it’s a molded plug with a transformer in it. I’ve added pictures for help
image.jpg
 
off 1 cooker outlet to 5A FCU then to socket as it's unlikely that the plug in PSU is fused
 
Getting 2 * 6mm in to one of the existing switches for a spur is going to be difficult.

If could put the new socket box adjacent to one of them so you could use a conduit coupler and two short bushes between them (so very little risk of cable damage) you could use a 1.5mm spur to a single 13A socket for the lights.

However going with the off side-mounted cooker outlet is going to be far easier and no additional box cutting and/or decorating to cover it up.
 
A socket-outlet could be connected to one of those circuits using 2.5mm² or as PC1966 says, even 1.5, although I personally would use 2.5 because it might be re-purposed later and there is more elbow-room with 2.5. The cable will be protected against overload by the nature of the socket, and against faults by the 32A MCB. All subject to the RCD of course.

I agree that some wall warts / adaptors that are not made to proper standards lack fusing, but that problem would be no different here versus plugged into the ring, plus a dodgy wall wart could be dodgy in other ways. So I wouldn't add an FCU to deal with that, I would bin it and get a proper one. It could possibly be replaced with and adaptor / PDE driver that has a mains cable rather than a plug, so that it could be wired into an FCU.
 

Reply to Spur of a Cooker unit for under cabinet lighta in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
678
Hi I have a switched fuse spur where the cooker hood should plug in to… above the actual cooker. I was wondering if I could swap this out for a...
Replies
7
Views
605
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
405
I have three Aurora Fluorescent linkable (linked) under cabinet 'strip' lights (c.21cm each) under the kitchen cabinets and over the sink area...
Replies
2
Views
334
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
870

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock