There is a recommendation that loads of 2Kw and above need to be on their own dedicated circuit, not fed via a 13 A spur
I think we've established that this wont be on a 13A spur... its on a radial, wired in 4mm, which could have a 32A OCPD if someone changes it back from a 16.

As above, if you want to isolate the outside sockets, then a 45A double pole switch ... (for a cooker or shower - no fuse) before going outside will suffice.


Edit, Afterthought: If youre doing any work to this circuit, you must ensure it is RCD protected... i dont think it was mentioned on the OP
 
Last edited:
There is no reason why it cannot be extended in 4.0 and upgraded to 32A however as previously mentioned the installation method may not permit it. If you are going to contain this cable in conduit then 32A is not an option.
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
spot on.
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
How is the new cable going to be installed.
 
How is the new cable going to be installed.
…was planning to run 4mm SWA to the new sockets. Had planned to use a short run (approx 1 metre) of 4mm twin and earth in a conduit between the two sockets rather than use SWA between the two sockets. Is 4mm T&E permissible in conduit over this short distance?
 
…was planning to run 4mm SWA to the new sockets. Had planned to use a short run (approx 1 metre) of 4mm twin and earth in a conduit between the two sockets rather than use SWA between the two sockets. Is 4mm T&E permissible in conduit over this short distance?
Contained in conduit it would not be rated at 32A unless it is singles.
 

Reply to Spur off a 4mm twin and earth, 32amp radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
295
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
756
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
DIYer question. I have a 32 amp supply going from consumer unit in garage to kitchen. It supplies an induction hob only. The cable is easily...
Replies
34
Views
3K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock