Discuss SWA armouring as Earth in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
At what size of SWA cable are you required to run an external earth ? I'm inspecting a distribution system and its a complete mess. No main earths anywhere but they have utilized the armour and are using at is their earth. I can't find anything in the regs book, is there possibly something in the guidance notes I can refer to ?
 
Hi Paul - if you've got GN8 its Appendix B. There's a few tables, this is just the first one. Hope that helps :)

IMG_0722.JPG
 
At what size of SWA cable are you required to run an external earth ? I'm inspecting a distribution system and its a complete mess. No main earths anywhere but they have utilized the armour and are using at is their earth. I can't find anything in the regs book, is there possibly something in the guidance notes I can refer to ?
SWA CPC.pdf
 

Attachments

  • SWA CPC.pdf
    991.5 KB · Views: 28
If you are doing inspections you should know this being an electrical supervisor and all that.
 
At what size of SWA cable are you required to run an external earth ? I'm inspecting a distribution system and its a complete mess. No main earths anywhere but they have utilized the armour and are using at is their earth. I can't find anything in the regs book, is there possibly something in the guidance notes I can refer to ?

There is no limit on size where a separate conductor is required, it depends on the individual conditions of the installation.
When assessing an existing installation the table 54.7 can be used as a first reference, but if this shows that the armour is inadequate you must then use the adiabatic equation as that may show that it is adequate.
Table 54.7 often gives a larger conductor size than is actually required.

You also need to consider whether the cpc also needs to perform the function of a bonding conductor, this usually changes things considerably.
 

Reply to SWA armouring as Earth in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
752
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock