Discuss switchgear for lift in the Australia area at ElectriciansForums.net

R

russells

Hopefully this one will be a simple one to answer.

A lift in a premises as been determined as a fire lift (to be used in evacuation under fire conditions)
the lift as to have 2 supplies of power, with basically switchgear (not provided in the lift electrics) that would simoultaneously cange the supply if one of the cables supplying was burnt out.

So this is the situation, we have a mains board in a building with plenty of spare ways in the board, and capacity, we will run two single phase supplies from this board to the lift motor room (by the way the fuseboard cupboard, and the lift motor room have enhanced fire protection) the cables have to go through different routes in the building fabric to get to the motor room (basically have a fire compartmentation drawing of the building and cabling must take different routes in different fire zones) (fire officer happy with this so).

My question is what switchgear do we have in the motoroom, we obviously have two cables from the same fuseboard that will go through a changeover switch, one cable will be master(either one) and one will be slave. the need will be for the power to not be interupted to the lift.

it is possible that we could use a manual type switch, again what would this switch be called, does this exist.

I am not an electrician but a construction manager, this problem is looming in the near future, this isnt in original building spec and will have to cop the cost our electrical contractor is going to wrap me up in smoke and mirrors and try and charge me a fortune so hopefully can gather as much information as possible.

Welcome any questions, and of course answers.

Russell
 
Both supplies coming from the same board but taking different routes to the proposed motor room.
What happens if the fire breaks out in the location of the board?
 
Trev

If the fire breaks out at the actual board then that will obviously cut out both supplies, however the fire zone will be identified as in the board and the evacuation plan would be not to use the lift. (there is very detailed fire strategy training for all staff)

it is a nursing home with a two storey lift in a almost remote extension, (remote being they are linked by a passageway, glazed corridor).....and before somebody points out, one cable will run internally, and one will run on the wall externally at eaves, (so as two give fire compartment seperation)

Russell
 
Both supplies coming from the same board

That's what I was thinking Trev,
usually they have to come from two different DB's and usually one is a backup supply/essential supply (Generator or otherwise), this falls under safety/life support regs.

I would try and get some more information first, before deciding anything.

Some other posters on here will have more experience of these things.
 
An automatic transfer switch will cost you a bomb and even then your supply is not guaranteed

Why cant they use a battery powered secondary system
 
I have built the auto transfer part before, this is not a major problem,

but it is the problem of the second supply and all of the associated additional building/safety/fire regs which will be the problem
 
Hopefully this one will be a simple one to answer.

A lift in a premises as been determined as a fire lift (to be used in evacuation under fire conditions)
the lift as to have 2 supplies of power, with basically switchgear (not provided in the lift electrics) that would simoultaneously cange the supply if one of the cables supplying was burnt out.

So this is the situation, we have a mains board in a building with plenty of spare ways in the board, and capacity, we will run two single phase supplies from this board to the lift motor room (by the way the fuseboard cupboard, and the lift motor room have enhanced fire protection) the cables have to go through different routes in the building fabric to get to the motor room (basically have a fire compartmentation drawing of the building and cabling must take different routes in different fire zones) (fire officer happy with this so).

My question is what switchgear do we have in the motoroom, we obviously have two cables from the same fuseboard that will go through a changeover switch, one cable will be master(either one) and one will be slave. the need will be for the power to not be interupted to the lift.

it is possible that we could use a manual type switch, again what would this switch be called, does this exist.

I am not an electrician but a construction manager, this problem is looming in the near future, this isnt in original building spec and will have to cop the cost our electrical contractor is going to wrap me up in smoke and mirrors and try and charge me a fortune so hopefully can gather as much information as possible.

Welcome any questions, and of course answers.

Russell

please remember your responsibilities my friend, as there was an incident recently, where a back up supply was not adequate and a young man died (his respiratory equipment stopped working), when the power failed. I beleive that the HSE will sucessfully prosecute the people responsible.

IMO the above would have been avoided, had an automatic generator been supplied to the premises in question.

If a fire causes a short circuit to any one of the cables from the same board, then it is likely that the breaker supplying that board will trip, unless your discrimination is spot on.

IMO, it is well worth exploring the possibility of a backup generator
 
At moment fire officer is happy that both supplies will come from same dis board, both supplies need to be dedicated from mains board and this is only option anyway. (obviously we could have another power supply from our proivider....again cost!!)

(automatic transfer cost a bomb says des56,)(not sure about battery supply, )


What would you call a manual changeover switch??
 
johnboy,

The home does have a backup generator supply, this is a manual changeover, the periodic inspection of this equipment and is fine, its not my baby anyway, i am a contractor building a new extension were the existing building as capacity to run the new extension,

the client as payed a fortune for fire consultation and this is what we have to provide, as i have said i am just trying to stay one step ahead of the costs from my electrical contractor, by being savvy about the cost and the options.
russell
 
What about an uninterruptible power supply? expensive I know but the advantage could be that if main power fails then back up power kicks in almost immediately, no need to go looking for the guy who knows where the manual changeover switch is in the dark etc
 
Again trev, the generator back up for the home is non of my buisness, It meets with the CQC who are the body that give them the ticket to operate the home (care Quality commision)
 
My Final piece of advice Russell, is to get everything in writing and not just verbal.

I understand the 'mechanics' of changeovers etc. but Iam not clued up on the legal aspects.
 
That's what I was thinking Trev,
usually they have to come from two different DB's and usually one is a backup supply/essential supply (Generator or otherwise), this falls under safety/life support regs.

Not done this sort of Install for a long time, but when we were doing them the Lift allways had 1 primary supply from the Mains & the Back up was from a Generator, switchover was allways Automatic, Never Manual.

In the event of a fire or other Emergency where power goes out but you need the Lift for evacuation you can't rely on someone remembering to go and do the switch over, possibly risking their lives in the process.
 
Id suggest automatic change over for the generator and running second supply from genny db most backup gennys iv seen only have anuto change over BUPA Homes have a genny hookup not an onsite genny tho
 
ok theree may be some discussion to the whole set up being not normal etc.

the question remains, what name for switchgear, name of automatic switchgear, name for manual switchgear.

I need to start looking at costs for switchgear, but do not know what to search for.

just on a note, the management of a fire situation in this home, (like many others) is a controlled evacuation, the staff have very thorough training and the whole building infrastructure, both the existing and the new have enhanced measures for ,
1. Ignition of a fire being incredibly unlikely (obviously arson is never considered in the fire equation as you just cannot build in measures.) combustible material as been risk assessed an non combustible replacements are prefered.
2. fire fighting equipment both manual estinguishers, and a sprinkler system. (fire fighting training to all staff)
3. fire alarm and zone reference panels at strategic and nursecall points.
4. mag locks, overhead automatic door closures to all bedrooms, fire compartmentation enhanced over what part B LABC determines.

The risk is taken very seriously, and managed very seriously.

Russell
 
Generally when we have built this kind of switch gear, it is just called an Auto Changeover,

As several of the posters have already said, this will be located at a point where the person responsible for safety/fire/building control deems to be suitable, the supply cables taking two different routes, depending on the zoning of the building.

As I already have pointed out the PIR for this is subject to different rules than BS7671, and may fall under various different Statute laws, which I cannot advise on.

This is a complex and specialist problem on so many levels, and costs may not be a consideration for parts of this.

Netblind Paul and several other contributors on here may be able to give you a more in depth answer.
 
Last edited:

Reply to switchgear for lift in the Australia area at ElectriciansForums.net

Similar Threads

I'm an electrical engineer in training so please bear with me. Basically, a bank has ordered a second 500kw diesel generator and my job is to...
Replies
3
Views
913
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
640
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
664
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
185
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
873

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock