Discuss Switchgear testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
0
Hi,

I run an electrical testing company mainly doing EICR for schools, hosptitals etc and am incresingly getting asked to do switchgear testing for the facilities.
Anybody help with level of training and standards required to do this? Any info on companies wich provide training would be a great help,

cheers
 
If you're talking about main LV switchboards fed direct from Distribution TX's then you are in a whole new ball game i'm afraid, where you will need to know your onions along with how to setup and test protection relays. The bigger and more complicated the Switchboard (eg Switchboards connecting several TX's with bus couplers galore and Stand-by generators thrown in for good measure) the further out of your depth you're going to be. Compared with testing and commissioning LV/MV Switchboards, a BS7671 EICR is a proverbial walk in the park!!


You'd need to be conversant with the various protection relays, how they are integrated into the system and work. You'd also need to be conversant with both primary and secondary injection test equipment, and those bits of kit don't come cheap at all. In fact, to cover the cost of the test equipment alone you'll probably be looking at the very least £12K and probably more, for secondhand or cheap budget test equipment!!

To give you an idea, take a look at our sponsors site. then look up ''Primary Injection'', ''Secondary Injection'' ''Ductor testers'' and depending on how deep you intend offering testing services, a good deal more on top!!

As to where you would gain training, pass i don't know. Most of the guy's we have used over the years have come from backgrounds in switchboard manufacturer, and have quite an extensive knowledge of all the protective relay manufacturers products etc. This field of work is so diverse and varied, it's hard to put any hard and fast minimum training and degrees of experience required.

This is a truly specialised area. Get into it, and make a name for yourself, ...and you can make some very serious money!! As you will be in demand from every major and not so major project around the world!! lol!!
 
If you're talking about main LV switchboards fed direct from Distribution TX's then you are in a whole new ball game i'm afraid, where you will need to know your onions along with how to setup and test protection relays. The bigger and more complicated the Switchboard (eg Switchboards connecting several TX's with bus couplers galore and Stand-by generators thrown in for good measure) the further out of your depth you're going to be. Compared with testing and commissioning LV/MV Switchboards, a BS7671 EICR is a proverbial walk in the park!!


You'd need to be conversant with the various protection relays, how they are integrated into the system and work. You'd also need to be conversant with both primary and secondary injection test equipment, and those bits of kit don't come cheap at all. In fact, to cover the cost of the test equipment alone you'll probably be looking at the very least £12K and probably more, for secondhand or cheap budget test equipment!!

To give you an idea, take a look at our sponsors site. then look up ''Primary Injection'', ''Secondary Injection'' ''Ductor testers'' and depending on how deep you intend offering testing services, a good deal more on top!!

As to where you would gain training, pass i don't know. Most of the guy's we have used over the years have come from backgrounds in switchboard manufacturer, and have quite an extensive knowledge of all the protective relay manufacturers products etc. This field of work is so diverse and varied, it's hard to put any hard and fast minimum training and degrees of experience required.

This is a truly specialised area. Get into it, and make a name for yourself, ...and you can make some very serious money!! As you will be in demand from every major and not so major project around the world!! lol!!



Thanks for the replies guys, gives me food for thought

cheers
 

Reply to Switchgear testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm an electrical engineer in training so please bear with me. Basically, a bank has ordered a second 500kw diesel generator and my job is to...
Replies
3
Views
900
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
837
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
728
Hi Guys, looking at doing Initial and Periodic inspecting and testing. Looking between the CandG and EAL Just wondering if I can ask peoples...
Replies
16
Views
664
I am currently going self employed. I was never put through any 18th edition courses, so have booked myself onto my 18th wiring regs. I want...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock