Discuss Testing ze at the origin in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

joel89

-
Reaction score
14
Hi all I'm an industrial sparky on maintenance doing my eal initial verification exam tomorrow was just wondering when doing ZE at the origin, do you do Neutral L1,L2,L3 and then Earth L1,L2,L3 and N+E ? Or is there between phases too? And is this the same for The PFC?
 
Earth L1,L2, L3 and put the highest reading down and should be done with the power switched off and the main earth disconnected to eliminate parellel
earth paths
 
Thanks Nick. Just for the ZE this yes? What about the PFC.? So I'll drop croc clip on earth incomer after disconnection and goes across phases yes?
 
It' begins with an M can't think off top of my head it's not megger, it's what the training centre borrowed us, it's on a domestic rig im involved with control panels mainly on the industrial side. Do a bit of installation work just never really done testing since college 7years ago!
 
Ole !
I've been getting to do ZE tests. :stooge_curly:
Using a megger has a 2 lead option and it gives you the Prospective Fault Current (PFC) at the same time.
 
Why would you want to rethink? Are you referring to the fact that the fault current under short-circuit conditions in a 3-ph system is significantly higher than the line-earth fault current?

No mate, it is because PEFC is taken with all bonding conductors and CPCs connected, Ze is taken with the Earthing conductor disconnected from the rest and measured on it's own.

PSSC is a different measurement. ;)
 

Reply to Testing ze at the origin in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
699
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
657
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
658

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock