Discuss Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

L

lamb.a

When using a meter to carry out earth loop impedance measurement on final circuits by disconnecting the earth conductor. Is it neccessary to check the line to neutral impedance, this should be carried out with all earths connected.
 
Hey.

Dont quite understand your post.

You only disconnect the main earth to carry out the Ze measurement at supply tails with main switch open and all circuits de-energised.

The measurement on final circuits that you describe is Zs and this is done with all earths connected and circuits energised

Please clarify??

Cheers:D
 
are you talking about a pfc measurment

:D didn't read the final circuit bit, beer goggles
 
Last edited by a moderator:
When using a meter to carry out earth loop impedance measurement on final circuits by disconnecting the earth conductor. Is it neccessary to check the line to neutral impedance, this should be carried out with all earths connected.


If you disconnect the earth conductor you would not have a path to obtain the Zs of the circuit.

Why would you want to do a line/neutral impedence test on a final circuit?

This is only done at the point of supply to find to find which of the fault currents is the higher.
 
Hey.

Dont quite understand your post.

You only disconnect the main earth to carry out the Ze measurement at supply tails with main switch open and all circuits de-energised.

The measurement on final circuits that you describe is Zs and this is done with all earths connected and circuits energised

Please clarify??

Cheers:D
When you have a steel wired armour cable with a seperate earthing conductor the armouring provides a parallel path so how would you know if the earth conductor was properly connected - by disconnecting the earth conductor at the farthest point and with earth still connected at distribution unit using an impedance meter with test lead connected to this earth conductor confirms good earth path (circuit is live) reconnect check impedance of the earthing conducting the steel wired armour gland. Use the lowest voltage if three phase and devide by 1.732 and divide the highest impedance to check prospective earth fault current. These swa cables feed dedicated equipment just wanted to confirm if line neutral tests required. Thanks
 

Reply to Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
704
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
I've just picked one of these up on a famous auction site. The voltages, low and high resistance ranges all appear to be working fine but it's not...
Replies
7
Views
295
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
580
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
856

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock