Discuss The Ring is dead, long live the Radial!⚡ in the UK Electrical Forum area at ElectriciansForums.net

There is a very strong requirement here for dead testing before the circuit is energized, both for a full installation and for simply adding a new circuit to an existing system. That applies for domestic, commercial and industrial stuff.

Not just IR testing to see if the cable is OK, but also testing R1+R2 (live and earth resistances) both to verify socket & SP switch polarity, and also from the boards Ze (earth loop impedance) to check the circuit's Zs value is going to allow fast enough disconnection by the choice of fuse or MCB, etc.
Me thinks they do things slightly differently in the US. Might be wrong.
 
Radials are usually quicker to install and quicker to test - so cheaper on labour, material wise breakers are same price and cable works out about the same or actually cheaper without the return leg.(Eg 30m of 4mm or 60m of 2.5mm) I do mainly commercial and use 25a 4mm radials a lot for runs along store walls etc. Also wiring rings in singles in containment is a massive pain to keep the right “leg” together and also twice as many drums to get tangled up and wrapped round your ladders ? rings have there place still, probably make more sense in houses and offices kitchens etc
 
When we buy a house later this year .I am doing a radial rewire . Might mean a huge consumer .But if possible will make every room radials etc
 
When we buy a house later this year .I am doing a radial rewire . Might mean a huge consumer .But if possible will make every room radials etc
my preference is rings for kitches/utility rooms. 2-3 radials for rest of house. (average house, not a mansion).
 
New posts

Reply to The Ring is dead, long live the Radial!⚡ in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
286
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
729
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
990
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock