Thanks so the IET is broken down into quite small publications where as BS7671 includes the whole lot in one publication.

Yes, it is explained in BS7671

I think he has just looked at table 54.7 without reading the regulations - as I suggested earlier.

there is NO requirement under the IEC version or the UK version that the cpc is the same size
 
I was always told by older sparks that Rings and reduced cpcs were due to copper shortages during the war....
Not exactly. They were introduced post-WW2 partly with a view to the shortages of materials, but also a surprisingly forward-looking realisation by the IEE that new homes would need far more outlets.

As a result it would be very wasteful to carry on with the pre-WW2 practice of many radial circuits with different fuse sizes at the DB and single unfused plugs (of which 2A, 5A, 15A and very rarely 30A existed in round-pin) depending on the appliance needs.

So the ring with one 20A or 30A fuse (as it was at the time) and many sockets due to diversity of use, and from which a common design of "13A plug" that could be fused 1,2,3,5,7,10 or 13A meant a far more efficient system.
 
slight variation on the theme, I had a roll of twin and earth recently and the cpc was insulated in green/yellow, made a change... I checked and turns out this is apparently standard in Ireland. suppliers had received wrong pallet and not realised. i think if it was put on sale over here it would sale. I would buy it as it saves sleeving.
It's about 30% dearer than standard T&E though. (Of course part of that is that there's a very limited amount made due to I.S. 201 cable being for such a small market. The other major factor is the extra copper content.)
 
It's about 30% dearer than standard T&E though. (Of course part of that is that there's a very limited amount made due to I.S. 201 cable being for such a small market. The other major factor is the extra copper content.)
The copper content often dominates cost these days.

Do you have an idea why the Irish standards body went for equal size / insulated CPC?
 
The copper content often dominates cost these days.

Do you have an idea why the Irish standards body went for equal size / insulated CPC?
At a guess it was to harmonise with continental Europe, but that's just an assumption on my part. (Although it's different to the cable types used there. That said, NYM-J is also used frequently.)
 
Yes, it is explained in BS7671

I think he has just looked at table 54.7 without reading the regulations - as I suggested earlier.

there is NO requirement under the IEC version or the UK version that the cpc is the same size


Wait- I thought table 54.3 was mandatory when the adiabatic method isn't being used?
 
Waste time was a bit harsh but the money we save will eventually be lost to testing, where as if we used the same size CPC we would only need to test PEFC/Ze at origin like we do PSCC.

Nonsense, the same testing is required whatever the size of the cpc.
An equal size cpc requires testing exactly the same as a reduced size one does.
 
Wait- I thought table 54.3 was mandatory when the adiabatic method isn't being used?

Yes, but if you are wiring standard circuits using T&E then you will meet the requirements given by the adiabatic method.

Your question was along the lines of 'why is this cable produced' (with smaller CPC) - well because it is perfectly acceptable to install if you size it correctly.
 

Reply to Twin and Earth CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Good evening all, Some help with following would be much appreciated. A 20 Amp rcbo in a CU supplies an adaptable box on the outside wall of a...
Replies
17
Views
16K
My assessor said that the minimum CSA for a Main earthing conductor for a TT was 16mm. I questioned this as I thought it was 4mm. Regulation...
Replies
30
Views
11K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top