Continuity but it would be a bit pointless proving it's of adequate size when we would already know it was.

Proving it is of adequate size is done by calculation before you start installing.

Zs proves continuity of the complete return path back to source using a higher current than is normally possible with a dead test.
 
All I'm saying is if the CPC was the same size your concern that ADS could take place would be as much as your concern that a short Line to Neutral would trip the MCB - basically we don't even think about it because we know the Line and Neutral are of the same size so it doesn't even cross our minds we take it for granted.
 
All I'm saying is if the CPC was the same size your concern that ADS could take place would be as much as your concern that a short Line to Neutral would trip the MCB - basically we don't even think about it because we know the Line and Neutral are of the same size so it doesn't even cross our minds we take it for granted.
Unlike Line to neutral faults, line to earth faults increase the risk of dangerous mains voltage appearing on exposed conductive parts, which is why we are required to test that disconnection times are met and that earthing and bonding is correctly maintained through out the installation.
The regulations talk about that if a circuit downstream of an rcd is installed, then as long as continuity of the protective conductor is confirmed by adequate testing and that the rcd has been confirmed to provide ADS, then yes measuring earth fault loop impedance is not necessarily required on rcd protected circuits, regulation 643.7.1
 
Last edited:
I don't want to get bogged down but Ireland are now using T&E with full size CPC aren't they?

I mean I'm not bothered but from a safety point of view a full size CPC obviously makes sense that much I think we can all agree.
 
I don't want to get bogged down but Ireland are now using T&E with full size CPC aren't they?

I mean I'm not bothered but from a safety point of view a full size CPC obviously makes sense that much I think we can all agree.
In the south, yes.
 
I mean I'm not bothered but from a safety point of view a full size CPC obviously makes sense that much I think we can all agree.

From a safety point of view it doesn't make a blind bit of difference as long as the CPC is at least equal to the minimum size required by calculation.

And you still need to carry out a Zs test whatever size you use.
 
Or course it makes a difference fault current should be carried away as quickly as possible.

and countrys that employee full CPC and adopted MCBs and RCDs earlier don't cry about sockets in bathrooms and carrying out Periodic Zs tests.

Skimping on CPC however you want to justify it, is cost over safety a practice that many countrys have left in the past where it bellongs.
 

Reply to Twin and Earth CPC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning All, Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC. Earthing is TNS with main bonding...
Replies
5
Views
1K
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
Good evening all, Some help with following would be much appreciated. A 20 Amp rcbo in a CU supplies an adaptable box on the outside wall of a...
Replies
17
Views
16K
My assessor said that the minimum CSA for a Main earthing conductor for a TT was 16mm. I questioned this as I thought it was 4mm. Regulation...
Replies
30
Views
11K
Hi all, first post, and it relates to quite a challenging installation. The short version is that I'm working through remedial work on a 75 page...
Replies
13
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock