Does no one have safety concerns for the spider in the pic?
 
Hum ..... let me quote from BYB p416

"If you are the person ordering the work, but not the owner of the installation, you should pass the certificate , or a full copy of it including the schedules, immediately to the owner"

17th Edition 632.1, AMD1, AMD2 & AMD3 Following the initial verification required by Chapter 61, an Electrical Installation Certificate, togetherwith schedules of inspection and schedules of test results, shall be given to the person ordering the work. These schedules shall be based on the models given in Appendix 6.

18th Edition 644.1 Except where Regulation 644.4.201 applies, upon completion of the verification of a new installation or an addition or alteration to an existing installation, including the replacement of a distribution board or consumer unit, an Electrical Installation Certificate based on the model given in Appendix 6 shall be issued to the person ordering the work.
 
So... my brother cannot see the spec of the SWA embossed on it anywhere, but has just measured the OD of it: actually only 12mm.
By my reading of the datasheets, that makes it 1.5sqmm x 2 or 3 core.
So the CCC of SWA is much higher than that for the equivalent T&E (or tri-rated cable that I'm familiar with), but 1.5 still tops out at 27 or 29A, and I'd like to bet that the MCB is 32A rated...
 
Also, we can now confirm that there is an SWA gland into the CU, but no gland into the isolator - which is fitted in an inaccessible void behind a kitchen cabinet, so is no use as an isolator i.e. just functions as a terminal box...
 
Think you are all forgetting who installed this cable, my take 2 core with a clip on the armour at each end for the cpc:rolleyes:
 
So... my brother cannot see the spec of the SWA embossed on it anywhere, but has just measured the OD of it: actually only 12mm.
By my reading of the datasheets, that makes it 1.5sqmm x 2 or 3 core.
So the CCC of SWA is much higher than that for the equivalent T&E (or tri-rated cable that I'm familiar with), but 1.5 still tops out at 27 or 29A, and I'd like to bet that the MCB is 32A rated...

Also, we can now confirm that there is an SWA gland into the CU, but no gland into the isolator - which is fitted in an inaccessible void behind a kitchen cabinet, so is no use as an isolator i.e. just functions as a terminal box...

Measuring the diameter is a bit hit & miss, a competent sparks would be able to assess the conductor size. In your picture, the swa looks bigger then 12mm OD, comparing it to the tw&e cables?

The isolator in 'an inaccessible void behind a kitchen cabinet', could you explain more, how is your brother expected to isolate the cooker?
 
Putting an isolator (and its screw connections) into an inaccessible void is not simply not ok. Oh Dear.
should be OK he can operate thew switch with a magnet
 
The CU end of the SWA has been glanded - but with a stuffing gland:
GetAttachmentThumbnail


Now I've received the pictures, I cannot identify what the 'allegedly SWA' cable really is - can anyone identify it from the image below?
GetAttachmentThumbnail
 
To be honest that cable doesn't resemble SWA the picyures aren't that informative, however it looks a bodge job to me
 
It could be SWA, the white part being the bedding and I think there is a blurry bit of grey that could be armourings. Looks of a small size to get that bend in the bedding if it is SWA. And it is obviously not terminated properly if so
 
looks like SWA as Andy says, with the bedding exposed, going to the isolator,and some stripped out inner from isolator to CCU. whatever it is, it's a complete abortion and needs ripping out.
 
I would suggest he reminds magnet that he is expecting certificates on competition ....
Agree, keep on to the boogers, reckon you would have a better than evens chance of getting legal costs if you prosecuted them.
 
Thank you Midwest. I agree, it looks like NYY-J cable, based on a quick google image search of that term. Must confess I'd never heard of the stuff, but that does explain the white inner jacket, no SWA glands, tight bend radii and small diameter.
So much for using armoured cable for the outdoor cable run then!
 
OP if your brothers not happy with the install. Put together a letter or an email of your concerns, and send it to the sales team, with whom you've made your purchase.

Ask them to address these matters. If that cable has a securing stuffing gland at one end, why hasn't it got one at the other, for example. The inner core should not be exposed.
 
It looks rushed in. you can easily wire PVC/PVC T & E through the voids and keep it neat. I think it could be 4.0mm 3 core SWA (I have had the jacket in SWA white) The SWA should be earthed at least one end SWA should be made off in some sort of compression gland.
 
We've now firmly established that the conductors are 2.5 sqmm. The spec is not embossed on the cable jacket where we'd expect to find it, but each of the 7 strands of copper in each of the 3 cores is around 0.7 mm in diameter, so πr² X 7 gives us 2.5 sqmm
 
We've now firmly established that the conductors are 2.5 sqmm. The spec is not embossed on the cable jacket where we'd expect to find it, but each of the 7 strands of copper in each of the 3 cores is around 0.7 mm in diameter, so πr² X 7 gives us 2.5 sqmm

Only person that actually clarify what spec this cable is, is the installer.
 
The job hasn't been signed off or certified yet. Anyway, I'm advising that my brother shouldn't accept this work.
The contractor was going to do the external run in T&E until my brother (a civil engineer by profession) insisted that SWA be used.
Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?
 
The job hasn't been signed off or certified yet. Anyway, I'm advising that my brother shouldn't accept this work.
The contractor was going to do the external run in T&E until my brother (a civil engineer by profession) insisted that SWA be used.
Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?
 
looks like SWA as Andy says, with the bedding exposed, going to the isolator,and some stripped out inner from isolator to CCU. whatever it is, it's a complete abortion and needs ripping out.
and i got a "bad spelling" for that by a member who's posted less than 30 times in 8 years. hmmm.
 
Cable Specification: NYY-J Mains and Control Cable Non Armoured manufactured to standard IEC60502-1 and VDE 0276-603 and available in sizes 5mm to 16mm and in 2, 3, 4, 5 and 7 cores. The cable features solid plain copper conductors, PVC insulated, PVC filler, PVC outer sheath. Black. 600/1000 volts grade to IEC60502-1 and VDE 0276-603. For installation indoors and outdoors as underground, or in cable ducts, installations with additional protection where mechanical damage is unexpected.

Am I reading this right?
 

Reply to Twin&earth and SWA installed loose on floor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
293
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
946
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
543
I have had a kitchen extesion built on an old property (c.1810), which has an unusual consumer unit situation. Part of the property has only a...
Replies
12
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top