Hum ..... let me quote from BYB p416
"If you are the person ordering the work, but not the owner of the installation, you should pass the certificate , or a full copy of it including the schedules, immediately to the owner"
Reg No?^^ did you not check the page in the BYB .....
So... my brother cannot see the spec of the SWA embossed on it anywhere, but has just measured the OD of it: actually only 12mm.
By my reading of the datasheets, that makes it 1.5sqmm x 2 or 3 core.
So the CCC of SWA is much higher than that for the equivalent T&E (or tri-rated cable that I'm familiar with), but 1.5 still tops out at 27 or 29A, and I'd like to bet that the MCB is 32A rated...
Also, we can now confirm that there is an SWA gland into the CU, but no gland into the isolator - which is fitted in an inaccessible void behind a kitchen cabinet, so is no use as an isolator i.e. just functions as a terminal box...
should be OK he can operate thew switch with a magnetPutting an isolator (and its screw connections) into an inaccessible void is not simply not ok. Oh Dear.
Or perhaps by telekinesis?should be OK he can operate thew switch with a magnet
Then if that' s all he gets, the kitchen company need to be taken to court for Malpractice.I think he will struggle for one of them, at best he might get a dubious minor works certificate....
Yes like most of themUnfortunately, Magnet insist on 100% payment up-front, so there is no option for my brother to withhold payment pending a adequate resolution, certs etc.
Unfortunately, Magnet insist on 100% payment up-front, so there is no option for my brother to withhold payment pending a adequate resolution, certs etc.
Agree, keep on to the boogers, reckon you would have a better than evens chance of getting legal costs if you prosecuted them.I would suggest he reminds magnet that he is expecting certificates on competition ....
It doesn't look like SWA to me either. Can anyone identify it?
you need to get out more. .Looks like NYY-J cable to me. A 3c 2.5 mm is 11.3mm, and 4mm is 13.1mm OD according to some links I've googled, with a 25A & 34A respectively.
you need to get out more. .
So much for using armoured cable for the outdoor cable run then!
So the SWA is not earthed.The CU end of the SWA has been glanded - but with a stuffing gland:
Now I've received the pictures, I cannot identify what the 'allegedly SWA' cable really is - can anyone identify it from the image below?
So the SWA is not earthed.
Sorry Midwest never used or seen it as far as I know.What if it is NYY-J cable.
We've now firmly established that the conductors are 2.5 sqmm. The spec is not embossed on the cable jacket where we'd expect to find it, but each of the 7 strands of copper in each of the 3 cores is around 0.7 mm in diameter, so πr² X 7 gives us 2.5 sqmm
The spec is not embossed on the cable jacket where we'd expect to find it
Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?The job hasn't been signed off or certified yet. Anyway, I'm advising that my brother shouldn't accept this work.
The contractor was going to do the external run in T&E until my brother (a civil engineer by profession) insisted that SWA be used.
Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?The job hasn't been signed off or certified yet. Anyway, I'm advising that my brother shouldn't accept this work.
The contractor was going to do the external run in T&E until my brother (a civil engineer by profession) insisted that SWA be used.
Civil Engineer=groundworker they are used to installing SWA for the electrical contractor so I suppose he knows it by default as outdoor cable.Just been looking at this thread again, and have to ask why would your Brother stipulate SWA?
Civil Engineer=groundworker they are used to installing SWA for the electrical contractor so I suppose he knows it by default as outdoor cable.