Any recognised / best practice methods / conduit types for routing cables under floor. I’m looking to feed an island kitchen unit so will be looking to supply an induction hob and sockets.
Will be a completely new floor with insulation on top of concrete, underfloor heating pipes, screed with stone tiles on top.
 
Stick 25mm2 galv conduits in and put a draw wire in, however if the supply to the hob needs to be more than 6mm you will have to think again, PS, make sure the conduit is in one piece without any couplers and make sure any bends flow and are not tight.
 
As MDJ has suggested, last one I did I ran the 20mm2 conduit from a 100mm galvanised box so I could connect T&E to singles and also earth the containment. The other end went straight to a double socket but again a galv box could be used.
 
As MDJ has suggested, last one I did I ran the 20mm2 conduit from a 100mm galvanised box so I could connect T&E to singles and also earth the containment. The other end went straight to a double socket but again a galv box could be used.
Presumably singles are easier to route through the conduit than T&E?
 
With regards to the whole situation im assuming its to be run in conduit for protection against physical damage, thermal damage etc? And also how come it has to be under the ufh?
Cheers guys

How else would you install the cables?

Apart from the ufh unnecessarily warming up the cables, the conduit etc might effect the heating screed/slab and possibly weaken it. You should check with the manufacturer, if you intend to do so.
 
Well through conduit im not a complete ****ing moron so no need for the sarcy response was simply asking for what other reasons than what id already stated. As ive said before im still training

I wasn't being sarcastic, I just asked a question? And I did reply to your second question, perhaps I shouldn't bother trying to help you anymore :)
 
Last edited:
I’d also be concerned that whatever containment is used, it is also water tight as kitchen floors do occasionally get wet.
 
Get your tin hat on sharpish mate , you'll be advised that conduit isn't designed to support additional weight of any sort apart from a very small spider- most likely with reg numbers quoted, and it would most certainly need a 50mm2 main bond back to the DNO transformer.:D
 

Reply to Underfloor conduit for kitchen island unit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
285
Hi all. I'm currently building an island in my kitchen which will contain a gas hob. I've cut a trench about 60mm wide from the edge wall to...
Replies
16
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
943
Hi, I'm getting renovations done to my home, including an existing extension which already has wet underfloor heating. We are moving a kitchen...
Replies
16
Views
4K
Hello guys, It’s my first post here so please be gentle :) I’m having a kitchen extension done and will have the hob and few powerpoints...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock