Roogy1

DIY
Reaction score
0
HI all, I've had 3 x additional gas supplies installed in a building. Can i use one 10mm bonding cable and link these new supplies (keeping the cable continuous by stripping the sheath and clamping into earth straps) or do i have to run 3 new earth cables? Also can i use a staple gun (metal uninsulated staples) to clip this cable to skirting ? Thanks in advance
 
Thanks, I forgot to add that these supplies are for 3 individual flats so I’m assuming that won’t make any difference?
that could depend on the flats' earthing arrangements. are they all to a common earth or separate?
 
that could depend on the flats' earthing arrangements. are they all to a common earth or separate?
The incoming supply comes into a boiler room at the rear of the property. There is a main earth bonding bar here where current water and gas pipes are bonded. The meters are located here. The electrical supplies to the flats go off in SWA cable via isolators
 

Attachments

  • A7C84F67-F64E-4F5C-ABB3-A17F72DAEF43.jpeg
    364.7 KB · Views: 11
It should be fine from the incoming supply that spits to the flats, as all flats are then on the same source and earthing arrangement anyway.

Check the bonding size though, as it would be determined in the PME case by the size of the incomer cable, not the size of the flat's feeders (see Table 54.8 in the regs).

For a couple of flats I would doubt the supply is more than 35mm (10mm bond), and very unlikely to be more than 50mm (16mm bond), so going with 16mm bond is probably OK, but check as far as you can as 10mm is cheaper and far easier to wrangle.

As already mentioned, ideally you don't want any joints in the bonding cable but if necessary then you can use something maintenance free like a proper crimp or soldered joint. Getting 16mm wrapped round your typical pipe clamp tag is difficult, you might need to have a longer screw/bolt than normally comes with them.
 

Reply to Using one cable for multiple Earth bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
854
Can you use metal staples to secure an earth bond cable to skirting
Replies
15
Views
2K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock