Discuss Using pipe work to bond to incoming water in the UK Electrical Forum area at ElectriciansForums.net

atm84

-
Reaction score
94
I have recently come across a situation whereby instead of running a main equipotential bonding conductor from the MET to the incoming water someone had instead ran a short bond from the MET to some copper pipe in the mains cupboard and clamped it and then placed a bond on the pipe near the incoming water (at the other end of the property) and bonded to the incoming water there.

Wander lead method states 0.02 ohms resistance.

I know this is not good practice but where does it say in the regs it has to be a continuous conductor and that you can't do it.
 
regs. specify that the bond to an incoming service should be within 600mm of the point of entry to the building, or as close as practicable. the scenario you describe might be fine as it stands, but when wet-pants comes along and cuts out some copper andreplaces it with that crappy DIY plastic crap, then you've lost your bond to the extarneous incoming service.
 
Obviously not a good idea as Tel says.
GN8 says that if the bonding is looped between services (e.g. MET to gas then gas to water) the the conductor should remain unbroken.
However 543.2 says that a bonding conductor can be a variety of different materials (many of which would require numerous joints) but do specify that the continuity of the bonding should be assured.
 
This could also be one of the occasions,where a visual,physical examination,could provide a better indication of possible issues,as 1x PFC is not available on the MFT :cyclist:
 
Guys cheers for the comments. I agree not ideal but I explained the scenario about the plumber coming along and cutting the pipe and the connection being lost. The section in GN8 certainly does say about the connection being unbroken however this reads as more of a 'recommendation' than a 'requirement' and describes a slightly different scenario.

I would never do it myself, I think it's poor practice but at the moment there is a bond. The resistance meets regulations blah blah blah. Would anyone give it a code when carrying out EICR?
 
The resistance meets regulations

The Regulations do not give a resistance to meet. If the resistance is that to be expected for the length and cross-sectional area of the cable you have then it is fine, otherwise something is wrong.
 
That's the bonding connection itself. Not the length of bonding cable. You can only work out what that should be by using the tables of resistance. Daz
 
There's a figure in GN3 but I'm not sure it's that one. Daz
 
Doesn't really provide the answer as to whether a copper pipe can be constituted as a main equipotential bonding conductor


Sent from my iPhone using Tapatalk
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk
 
That relates to a protective conductor not a main equipotential bonding conductor. No body has said if they would happily use a copper heating pipe as part of a main equipotential bonding conductor. What code would anyone apply?


Sent from my iPhone using Tapatalk


Yeah......look up the definition of a protective conductor!
 

Reply to Using pipe work to bond to incoming water in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Carrying out remedial work on a commercial site and I've come across a metal out building that has a water supply to it. The water pipe...
Replies
6
Views
1K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
480
This is my first post and I hope I explain it correctly/ Simply. 1100sq foot single family home, 100 amp service. I am having an electrician...
Replies
2
Views
900
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock