Search for tools and product advice,

Discuss ventilation within computer room in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
the computer server room is protected by a gas suppression system
apart from CRAC units, should a ventilation fresh air and extract system be installed in the room
 
the computer server room is protected by a gas suppression system
apart from CRAC units, should a ventilation fresh air and extract system be installed in the room
IT systems work better ar 50%RH and 70 degrees
 
May depend on the type of room and size. If it is a broom cupboard, no. If it is a fair sized room, it should have an extraction and over pressure vent, especially if it has a void ceiling or glass. Your gas contractor would normally advise on that though.

Edit: to be fair, even if it is a broom cupboard, if it warrants gas protection and you are going to the trouble of integrity testing, you should have an extraction system to remove smoke and extinguishant once the fire brigade have turned up, so yes, it should make up part of any gas protected zone.
 
Last edited:

Reply to ventilation within computer room in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
660
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
571
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
362
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
638
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
237

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock