Discuss Voltage drop calculation in the UK Electrical Forum area at ElectriciansForums.net

M

Missing-spark

Hello everyone just want a little help how you would calculate the volt drop if

230 single phase heater circuit
line & neutral conductors combined resistance of 0.68
Temperature at 20 degrees and load current of 16A?
show calculations


got this in my 2395 today wanna make sure I used the correct method
i ended up with a volt drop of 5.4 or 5.2 can't remember

please help thank you

i did 230 divided by 0.68 multiplied by 0.016
 
Last edited by a moderator:
Post up your workings and I'm sure someone will advise you.
 
With your values that would give you a volt drop of 13 volts which is not acceptable are your r1 rn value correct seems a bit high if it's right you need to increase the case of your cable

- - - Updated - - -

Csa of your cable
 
That's 3 marks lost then. Fingers crossed for my 2394 exam tonight. I'm good with the calculations just that one threw me cause I didn't have the length or mv/a/m

anyone else do the 2395 yday?
 
why complicate the issue. just use ohms law V=IR, i.e. 16 x 0.68
 
why complicate the issue. just use ohms law V=IR, i.e. 16 x 0.68

16 x .68 = 10.88V then adjust to 70 degrees (conductor operating temperature for 70 degree thermoplastic cable) by multiplying by 1.2 = 13.056V

To see if it falls within the allowable %
(13.056/230) x 100 = 5.68%
 
Last edited:

Reply to Voltage drop calculation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
779
Hello im currently doing the 2391 online I have failed 4 times but I realise there are variations to the voltage drop calculation could someone...
Replies
25
Views
4K
Hi Folks I've been trying to work out whether a doorbell will work with approximately 16m run of bell wire. I've tried to find out volt drop...
Replies
6
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock