Discuss What am I accountable for on CU change as got bad test results. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

PHS

-
Reaction score
4
Hi, all continuity test results are ok now I replaced all the loose earths in all the sockets and lamp holders around the house. The radial going off to feed the boiler/shower/not sure what else, all branches out of a old unfused spur where the neon no longer works, and this radial is where I am having problems with the insulation test. E/N is giving me 174, as is E/L would be nice to get the 999 reading though, but the L/N reading is showing a short. (0).
This is for a test piece to be examined and I only changed the CU, do I now need to locate and fix problem before i can carry on with my tests and have my assesment?
Cheers
 
I would have said you should have tested located any faults and corrected them before changing the board,as you are aware a fault exists it's up to you now to find and fix it,hence testing before you start.
 
the L/N short will be a connected load. if the 174 you mention is 174 Megohm, then just record it as such and move on.
 
I would have said you should have tested located any faults and corrected them before changing the board,as you are aware a fault exists it's up to you now to find and fix it,hence testing before you start.

So your talking a possible rewire of radial?
 
if this job is for scam assessment, just mention to assessor that yoiu have noticed the lower IR reading, but it's still way above the 1 meg. limit.
 
the L/N short will be a connected load. if the 174 you mention is 174 Megohm, then just record it as such and move on.

So find out where the third leg goes to, as 1 leg goes to boiler, 2nd goes to shower and a third shoots off under floor boards to something I couldn't locate when searching the house. I will need to search again and find it to see what's on it and disconnect
 
If the spur has a neon on it it is possible that the neon is now just connecting through as it is not working and giving you the reading.
Assuming there is nothing connected to that spur.
If you do not know where it is going how do you know you removed the loads?
Disconnect the unfused? spur and test each run of cables either way, but if L+N to E is OK then you should be OK.
 
If the spur has a neon on it it is possible that the neon is now just connecting through as it is not working and giving you the reading.
Assuming there is nothing connected to that spur.
If you do not know where it is going how do you know you removed the loads?
Disconnect the unfused? spur and test each run of cables either way, but if L+N to E is OK then you should be OK.

If I do (L/N) - E, I get a 181 reading
 
So the circuit is fine, carry on.
You are only making sure it is safe to reconnect.
You could do a continuity L+N and if you get 10 - 400 ohms ish then it is a piece of equipment connected.
It could be higher for electronics and stuff.
 

Reply to What am I accountable for on CU change as got bad test results. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
667
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Replies
3
Views
895
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock