Discuss What does the main fuse protect? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

rewireIT

Esteemed
Reaction score
190
From another thread:

The 60A fuse could be sized to protect the size of cable feeding the property, so having it changed to 100, or even 80, the middle size, might be impossible.

I'm thinking about this and it's got me all confuzzled.

Don't fuses protect anything downstream ie my laptop's charger has a fuse that protects the charger cable, the socket has a breaker that protects its wiring, the boards wiring has a main fuse that protects it from overload..... wouldn't protection for the supply cable be at the suppliers gear away from the house somewhere ie upstream?
 
No, at the transformer they my have say a 300A fuse per phase
this will feed a cable that runs down the street
from the cable in the street there will be multiple tap offs feeding each house.
I think about 50 or 60 homes fed from each cable.
 
wouldn't protection for the supply cable be at the suppliers gear away from the house somewhere ie upstream?

Yes,,BUT,,

As James has said, the local distribution cable leaving the substation has protection of 300a or whatever is appropriate for the cable.

Here's the BUT,,
When the cable to the property / house is taken off that cable it's CSA is dramatically reduced at 16mm² or 25mm² or whatever, so the 300a would not be suitable protected and in the U.K that joint is not in a position where it could be.

It would be the same as having a 20a protected radial wired in 2.5mm² with 0.5mm² cables directly joined onto it along the way, you'd need to protect those.
 
As @mainline says the DNO fuse is there to protect their cables from overload by anything down-stream of it (i.e. fault or excess demands by the installation). It need not meet the disconnection times that the regs demand for sub-m,ain, etc, as its purpose is not ADS for shock protection.
 
It would be the same as having a 20a protected radial wired in 2.5mm² with 0.5mm² cables directly joined onto it along the way, you'd need to protect those.
Would that apply to say an oven fan that has its supply cable in 0.5mm being fed from a 32amp supply ?
Or an alarm panel ?
 
There are two types of fault, short circuit ph-ph or ph-E and overload.
The fuse at the substation protects the distributor from a short circuit and from overload, it also protects the service from short circuits. The cutout fuse protects the service from overload only.
 
So on a kettle, is the fuse there to protect the appliance lead?

Cause i still don't understand how this is working.

There's an appliance load drawing on a cable, if load draws too much, fuse at the start of cable breaks, stopping flow, protecting appliances cable.

Load draws on double socket, draws too much, breaker in CU breaks to protect 2.5mm wiring into socket.

Entire load of house pulls too much on 25mm tails, main fuse goes.

That's how it's always been explained to me.

So it should then stand to reason that cut out is there to protect the installation wiring not the main incomer?

Again, i'm in the corner with the dunce's hat and a probably overthinking it.
 
Entire load of house pulls too much on 25mm tails, main fuse goes.

That's how it's always been explained to me.

So it should then stand to reason that cut out is there to protect the installation wiring not the main incomer?

Again, i'm in the corner with the dunce's hat and a probably overthinking it.

Tails will be sized according to cut out fuse and will indeed be protected by it, but that same fuse also protects reduced CSA DNO cable from overload by consumer.
 

Reply to What does the main fuse protect? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
710
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
750
Hi Everyone, I have a faulty smart meter, its broken since I moved in and I am putting all my effort to fix this, I am a tenant though. A...
Replies
5
Views
2K
Hi all, been reading around this and i have to admit ive quickly gone out of my depth as regards EV chargers. The charger in question is a...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock