Currently doing a design project in college and I need to pick a circuit breaker ( In device rating and type) for a food holding equipment unit that requires a 16A 400V three phase and neutral supply that is supplied by 5 core SWA. I think I should pick a 16A 3P+N RCBO but wasn't completely sure so thought I would run it by on here 1st before I write anything down.
 
What is the reasoning or requirement for an rcd?
It is also, unusual but not unheard of to have 4 pole circuit breakers for 3 phase equipment.
 
What is the reasoning or requirement for an rcd?
It is also, unusual but not unheard of to have 4 pole circuit breakers for 3 phase equipment.
well doesn't that circuit need to be protected like all the other circuits which are all rcbos so I thought it would be best for this to be a rcbo instead of a 3P+N MCB with a RCD. But am I right to use a 3P+N breaker for 3 phase though ?
 
Is the food holding equipment connected by way of a socket outlet, if so the rcd can be incorporated into the socket outlet. If not and fault protection is afforded by the mcb then rcd protection is not required unless manufacturer instructions suggest it and this must be taken into consideration.
 
well doesn't that circuit need to be protected like all the other circuits which are all rcbos so I thought it would be best for this to be a rcbo instead of a 3P+N MCB with a RCD. But am I right to use a 3P+N breaker for 3 phase though ?

You can't design an electrical installation by assumption, or just copying what else has been done.

As this is a college design project they will be looking for you to apply your knowledge of the regulations and circuit design process.

As far as RCD protection goes you should go through all the situations which require RCD protection and decide which ones, if any, apply to your circuit.
For example a circuit serving a room containing a bath or shower requires 30mA RCD protection, so as part of the design process you ask the question 'does this circuit serve a room containing a bath or shower?'

You should write this all down as part of the design process so that the person assessing your work can see what you have done and crucially will be able to help if you make a mistake.

As for a TP+N MCB, it would be unusual to need one, for the vast majority of three phase circuits a TP MCB is adequate, and arguably preferable.
 
We need to be careful here, we don't do homework but we can nudge you slightly so ask members not to dish solutions out but no issue in seeing their calculations/solutions and nudging in the right direction - we don't learn by copy and paste!
 
Hi ,
Currently doing a design project in college and I need to pick a circuit breaker ( In device rating and type) for a food holding equipment unit that requires a 16A 400V three phase and neutral supply that is supplied by 5 core SWA. I think I should pick a 16A 3P+N RCBO but wasn't completely sure so thought I would run it by on here 1st before I write anything down.
you don't need an rcd unless you are supplying the equipment via a socket outlet of 32A or less. If you are wiring through a local isolator to fixed or immovable equipment you do not need an RCD. A 16A tp mcb will do just fine probably type C
 
you don't need an rcd unless you are supplying the equipment via a socket outlet of 32A or less. If you are wiring through a local isolator to fixed or immovable equipment you do not need an RCD. A 16A tp mcb will do just fine probably type C
Assuming ADS is provided without the provision of an RCD.
 
well doesn't that circuit need to be protected like all the other circuits which are all rcbos so I thought it would be best for this to be a rcbo instead of a 3P+N MCB with a RCD. But am I right to use a 3P+N breaker for 3 phase though ?
only need an RCD device if you are supplying the equipment through a socket. Otherwise it's just a triple pole mcb and neutral isn't switched.
 
So guys , for example supply to 3phase roller shutter door motor with attached 1m lead , if socket was high level ( say 3.5m up ) controlled by low level isolator, would you still put it through an rcd ?
 
So guys , for example supply to 3phase roller shutter door motor with attached 1m lead , if socket was high level ( say 3.5m up ) controlled by low level isolator, would you still put it through an rcd ?

There is no exception for height or accessibility in the regulations.

The designer of the installation may do a risk assessment to justify not providing RCD protection if there is some reason why RCD protection may be undesirable.
 
You will need to now if there is start up current on the equipment. To choose what type of mcb / rcbo B C or D .Also Just wondering if 16amp ocpd is a bit close to the limit if the equipment demand load is also 16amps.
 

Reply to What type of circuit breaker would be used for a three phase circuit? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi, I'm doing my Level 3 Electrical Install course, and I'm doing distance learning so most of the work is being done by myself with no guidance...
Replies
1
Views
369
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
877
Hi there currently doing some diversity calcs for college work and had a query about what diversity factor to apply to a 16A 3 phase commercial...
Replies
3
Views
1K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
690
I live in Thailand and my home has 240v, 3 phase power supply. I want to add an electric car charger but first want to determine what the outlet...
Replies
0
Views
677

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock