Discuss Where to put main protective bonding conductor if no water mains isolation in house in the Australia area at ElectriciansForums.net

Reaction score
24
Hi all New to the site ! It ! brilliant. Its a real result to find such a community forum. great subjects and discussions, already been so helpful...

Thanks

So got this question. In house and to turn the water mains of its only from street. No mains isolation in house. so where would I need to put my main bonding? closest visible point of entry?

thanks
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

I recently had this discussion with my niceic inspector and in the regs it says where reasonably practical so if the meter or entry is far away then wherever you can get it
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

"reasonably practical" is the sensible approach too.

If I was you, I'd make sure it was somewhere "obvious" like under the sink in the kitchen (or where ever the water comes into the house) so if somebody is looking for it, at a later date, they should find it.
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

544.1.2
Shall be made as near as practical to the point of entry of that service into the premises


No internal stop tap,then no concern about being on consumers side
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

I thought the requirement was for the position to be within 600mm of where the pipe enters the building?
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

I thought the requirement was for the position to be within 600mm of where the pipe enters the building?

Yes this what i thought ! Thought Gas was suppliers side. still 600. OSG p29 Note 3
544.12

Pipe enters under floor. from what i can see its copper . without ripping any more boards up...so maybe plastic on entry. still asked plumber he pointed to the copper pipe.
SO yeah under floor. So could clamp where i got board up and then also continue that 10mm un broken to the nearest sink or visible point.
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

Not sure if my post comes over as I intended

My opinion is
The connection needs to be as close as practical to that point of entry and as has been stated within 600mm
Bonding in the kitchen,at the sink, when there is exposed pipework prior to that Kitchen sink is not the intention of the reg
 
Last edited:
Re: Where to put main protective bonding conductor if no water mains isolation in hou

Des 56 In your opinion if that kitchen sink is THE closest place to point of entry where visible are you saying its fair game
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

sorry I SHOULD SAY does regs imply this could be Ok?



If its the nearest practicable position then yes
If you are making that decision because its the most conveniant,then no

In the end it all boils down to the individual persons veiw on what is practical
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

If its the nearest practicable position then yes
If you are making that decision because its the most conveniant,then no

In the end it all boils down to the individual persons veiw on what is practical

Yeah i totally agree. convenient and practical do have a different meaning. convenience does not necessary have safety in its interests.
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

Is this post for real? Are all of you for real?

God damn it's been a long night.
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

where the water pipe comes into the property, above the floor, accessible position, get the plumber to fit a stop tap. this will a. give you a point to bond to. b. give you an accessible means of turning off the water supply incase of a leak, save going outside in the dark to isolate the water.
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

The whole point of keeping the bond connection as close to the entry of the building as possible is because of future alterations to the pipe work. If you bond the pipe work at 'entry' to the building then no matter what alterations are made then the pipe work will still be bonded. Bond it elsewhere then alterations in the pipe work may well disconnect the earth bond.

Hope Rocker and Spin are still giggling.
 
Last edited by a moderator:
Re: Where to put main protective bonding conductor if no water mains isolation in hou

There should be a label on the CU indicating where the bond is.
 
Re: Where to put main protective bonding conductor if no water mains isolation in hou

I bet they are really giggling now.....
 

Reply to Where to put main protective bonding conductor if no water mains isolation in house in the Australia area at ElectriciansForums.net

Similar Threads

Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
701
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
487
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock