Discuss 13A plug on a new 3.65 kW oven? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
We have a new Hotpoint oven to install SI4 854 PIX. Old oven was 2.8kW Neff hard wired into dedicated circuit with its own breaker switch on wall. However, new oven, with pyrolytic cleaner, is 3.65 kW, rated but comes with 13Amp plug and lighter gauge wiring. I was going to plug in myself but clearly I need a sparky to convert hard wired socket to plug socket. However, in any case, this seems wrong - surely this requires 16A fuse and heavier duty wiring?
 
33672D9C-27D9-41D4-AD90-43D1754932F8.jpeg
Data sheet says max current 13A. Where did the 3.65kW come from?
 
We have a new Hotpoint oven to install SI4 854 PIX. Old oven was 2.8kW Neff hard wired into dedicated circuit with its own breaker switch on wall. However, new oven, with pyrolytic cleaner, is 3.65 kW, rated but comes with 13Amp plug and lighter gauge wiring. I was going to plug in myself but clearly I need a sparky to convert hard wired socket to plug socket. However, in any case, this seems wrong - surely this requires 16A fuse and heavier duty wiring?
The 13 Amp fuse is there to protect the cable not the cooker circuit.
Your cooker/oven should have a breaker in the CU.
 
We have a new Hotpoint oven to install SI4 854 PIX. Old oven was 2.8kW Neff hard wired into dedicated circuit with its own breaker switch on wall. However, new oven, with pyrolytic cleaner, is 3.65 kW, rated but comes with 13Amp plug and lighter gauge wiring. I was going to plug in myself but clearly I need a sparky to convert hard wired socket to plug socket. However, in any case, this seems wrong - surely this requires 16A fuse and heavier duty wiring?[/QUOT
When i say cable ,i mean the cooker cable.
 
As @LeeH has pointed out. I can't find 3.65kW in any of the specs.
 
It may well be 3.65kW total. This usually consists of a fan element and a grill element, which cannot be used at the the same time, hence the 13A rating.
 
As @LeeH has pointed out. I can't find 3.65kW in any of the specs.

I suspect that figure comes from the rating label on the appliance. Seems all these manufactures don't want to get involved in the cabling for these appliances 'if in doubt, speak to a qualified electrician'!

All instructions now days seem to be obviously vague.
 
View attachment 41256 Data sheet says max current 13A. Where did the 3.65kW come from?
3.65kW is on label on packaging and also on sticker inside oven.

I have meanwhile phoned Hotpoint and although the support phone people were agreeable they knew nothing. They did however contact their tech people who replied, as another forum response indicated, that 3.65 kW is total load from all oven functions, but since this is an impossible scenario 3.65kW is never drawn at ay one time, and so 13A is fine. So seems all ok. BUT, I have to wonder ... what's the purpose of the 3.65kW rating? Surely a max possible kW would be more useful?

Thanks anyways guys. Will get a pro to convert to plug socket for me :)
 
3.65kW is on label on packaging and also on sticker inside oven.

I have meanwhile phoned Hotpoint and although the support phone people were agreeable they knew nothing. They did however contact their tech people who replied, as another forum response indicated, that 3.65 kW is total load from all oven functions, but since this is an impossible scenario 3.65kW is never drawn at ay one time, and so 13A is fine. So seems all ok. BUT, I have to wonder ... what's the purpose of the 3.65kW rating? Surely a max possible kW would be more useful?

Thanks anyways guys. Will get a pro to convert to plug socket for me :)
Think you may have been fobbed off
 
The Rating plate should indicate what the power of the cooker is, to say it was on the packing, may be true, but the plate should have indicated that as well.
 
convert the cooker outlet to a BS1363 socket. plug it in, switch on as much as you can ( on the oven ) and clamp the line cable off the MCB. (and see if the plug top gets hot. :eek:).
 
3.65kW is on label on packaging and also on sticker inside oven.

I have meanwhile phoned Hotpoint and although the support phone people were agreeable they knew nothing. They did however contact their tech people who replied, as another forum response indicated, that 3.65 kW is total load from all oven functions, but since this is an impossible scenario 3.65kW is never drawn at ay one time, and so 13A is fine. So seems all ok. BUT, I have to wonder ... what's the purpose of the 3.65kW rating? Surely a max possible kW would be more useful?

Thanks anyways guys. Will get a pro to convert to plug socket for me :)

I suspect, I might be wrong, that CE or EU or Brexit regulations require total load of an appliance, you've probably chucked out the numerous energy level/product data sheets and other completely useless documents that accompany appliances, such as these. In your case, as Andy stated, you can't turn everything at the same time. My old range cooker, had a lower rating, managed on a bit of 1.5mm flex and took 12hrs to cook the Sunday Roast.
 
Why have I been fobbed off?

See you've been two timing us with another forum :rolleyes:

Think that's all you'll get from a manufacturer, not bad advice?

I might be minded to do what Murdoch suggested, if the manufacturers allows, cut off plug & connect to the existing cooker outlet.
 

Reply to 13A plug on a new 3.65 kW oven? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I purchased a new-build apartment 10 years ago, which came with a fitted oven and microwave. Both appliances are described by the manufacturer...
Replies
1
Views
762
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
950
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
800
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock