Search the forum,

Discuss Band 1 cabling covered by BS7671 in the UK Electrical Forum area at ElectriciansForums.net

Status
Not open for further replies.
Reaction score
39
Hi All

Just wondering if the installion method of band 1 cabling is covered by BS7671?

I'm pretty sure it isn't but just been told that alarm conduits have to be secured with metal fixings. Just need to find some evidence in the regs to support this.

Cheers
 
How does this work for you....

110.1.2 The Regulations include requirements for:
(i) circuits supplied at nominal voltages up to and including 1000 V AC or 1500 V DC. For AC, the preferred frequencies which are taken into account in this Standard are 50 Hz, 60 Hz and 400 Hz. The use of other frequencies for special purposes is not excluded
(ii) circuits, other than the internal wiring of equipment, operating at voltages exceeding 1000 V and derived from an installation having a voltage not exceeding 1000 V AC, e.g. discharge lighting, electrostatic precipitators
(iii) wiring systems and cables not specifically covered by the standards for appliances
(iv) all consumer installations external to buildings
(v) fixed wiring for information and communication technology, signalling, control and the like (excluding
internal wiring of equipment)
 
Last edited by a moderator:
Are Band 1 Cables less likely to be the cause of entanglement over any other cables?

I think there's only one answer.
 
  • Like
Reactions: DPG
Hi All

Just wondering if the installion method of band 1 cabling is covered by BS7671?

I'm pretty sure it isn't but just been told that alarm conduits have to be secured with metal fixings. Just need to find some evidence in the regs to support this.

Cheers

Yes it is covered by BS7671, and even if it isn't then you should be fitting metal supports regardless.

Metal supports for wiring systems was brought in because firefighters burned to death after getting tangled in cables which fell down during a fire.
 
Are you thinking separation.
No, just the metal fixing side of things.
[automerge]1584649179[/automerge]
Yes it is covered by BS7671, and even if it isn't then you should be fitting metal supports regardless.

Metal supports for wiring systems was brought in because firefighters burned to death after getting tangled in cables which fell down during a fire.
I know why you use metal fixings I wasn't asking that, I was just asking if ELV was covered by BS7671
 
Last edited by a moderator:
I know why you use metal fixings I wasn't asking that, I was just asking if ELV was covered by BS7671

Yes it is, if you get a copy of BS7671 and read the section which sets out what it covers you will see this.
 
  • Like
Reactions: DPG
Status
Not open for further replies.

Reply to Band 1 cabling covered by BS7671 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
757
Hi, Just been looking into powerline adaptors and just wondering how they work. I read that they operate on far higher frequencies to mains...
Replies
4
Views
1K
Hi, I'm running a 70ft underground UF cable in 3/4 inch PVC conduit to 2 sheds. The sheds are 3ft from each other. I'm just a DIYer enthusiast so...
Replies
1
Views
776
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
239
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
537

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock